Isn't PEX used as the piping in heated floors where you would have a large
change in temperature from winter (using it to halt the floor cum building,
and summer where you wouldn't?


On Fri, Oct 7, 2016 at 6:31 AM, Steve Leyton <[email protected]>
wrote:

> I think an investigation of the potential for thermal expansion would be
> prudent. The applications I described topped with 3-8 feet of earth, so
> temperatures were stable year-round.  But PEX is designed to expand and
> contract without loss of structural integrity, so it's well suited for
> embedment in concrete.
>
>
> Steve
>
>
> -------- Original message --------
> From: Ben Young <[email protected]>
> Date: 10/7/16 6:27 AM (GMT-08:00)
> To: [email protected]
> Subject: Re: Monolithic domes
>
> I thought about PEX as well Steve, its no four letter word for me.  At
> least with the CPVC we can comply with the pipe requirements from NFPA 13,
> which would require less 'selling' than PEX use.  Although as Mark points
> out about thermal expansion, PEX does have a lower rate of I think about an
> inch per 100 feet.  Because the concrete acts as a thermal sink and they
> are insulated on the outside, I think the temperatures inside are
> incredibly stable.  The Wikipedia page for these things makes them sound
> incredibly attractive for almost any building type, but there are some
> drawbacks.
>
>
> I'm just really surprised at the complete and utter lack of information on
> sprinklering these except for the one I posted.
>
>
> Benjamin Young
>
> On Thu, Oct 6, 2016 at 10:41 PM, Steve Leyton <[email protected]>
> wrote:
>
>> Listed PEX A and I think the sprinklers were screwed right into the
>> branch fittings because we only needed 30 minutes per UL 1821. If you
>> really need the details, I have to look at my technical report and may not
>> be able to do that for a couple days as I'm taking a long weekend.
>>
>> Wine caves are a little different than overhead domes because we ran a
>> CPVC main down the corridors under the floor and branched off with 1" PEX
>> that wrapped halfway around the vault serving a single sprinkler. The CPVC
>> was directly buried and the floors were made of hand-laid stone on a sand
>> bed.
>>
>> But I think you could drop to the sprinklers with CPVC or even use PEX
>> because I'm not as worried about protecting piping that has a sprinkler
>> between it and the heat source as I might be concerned about a piping span
>> that's between sprinklers.
>>
>> Steve
>>
>>
>> -------- Original message --------
>> From: AKS-Gmail-IMAP <[email protected]>
>> Date: 10/6/16 7:23 PM (GMT-08:00)
>> To: [email protected]
>> Subject: Re: Monolithic domes
>>
>> If I may ask, was that PEX A or B and how were the last bit of drop
>> piping handled where the sprinklers screwed in?
>>
>> Allan Seidel
>> St. Louis, MO
>>
>>
>> On Oct 6, 2016, at 3:32 PM, Steve Leyton <[email protected]>
>> wrote:
>>
>> It’s a dirty word on this Forum to some, but I would consider looking
>> into PEX tubing if you can get it to work hydraulically.  The challenges
>> with PEX are smaller ID and temp/pressure rating.   However, PEX can easily
>> be attached to the formwork for concrete or Gunnite and we have used it
>> with great success in wine caves out here on the Left Side.    Aggregate
>> concrete has a fire resistance rating that can be extrapolated as about
>> 22.2 minutes per inch and I’ve done tech reports for two wine cave
>> applications where we obtained equivalency approval for this application.
>>
>> Steve Leyton
>>
>>
>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>> @lists.firesprinkler.org <[email protected]>
>> ] *On Behalf Of *Maurice Marvi
>> *Sent:* Thursday, October 06, 2016 12:58 PM
>> *To:* [email protected]
>> *Subject:* re: Monolithic domes
>>
>> Repairing buried CPVC branch lines sounds like fun.
>> Not.
>>
>>
>> Maurice Marvi
>> ------------------------------
>>
>> *From*: "Ben Young" <[email protected]>
>> *Sent*: Thursday, October 06, 2016 3:18 PM
>> *To*: "[email protected]" <
>> [email protected]>
>> *Subject*: Monolithic domes
>>
>> Does anyone have any information at all about putting sprinklers in a
>> concrete monolithic dome?
>>
>> I was able to find one article about it at the monolithic dome
>> institute's website here:
>> http://static.monolithic.com/construction/sprinklers/index.html
>> Looks crazy, but also interesting.
>>
>> Benjamin Young
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>>
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)