I have never actually seen one but
I do recall rumblings about fire pumps starting to have an option of grooved 
suction and discharge outlets a few years ago.
Mark


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike B Morey
Sent: Thursday, December 15, 2016 6:34 AM
To: [email protected]
Subject: Re: NFPA 20 & Suction Flanges - Character set not allowed

NFPA 20 2013: 4.13.2.1 Sections of steel piping shall be joined by means of 
screwed, flanged mechanical grooved joints or other approved fittings.
NFPA 24 2013 10.3.3 Groove Joining Methods.  Pipes joined with grooved fittings 
shall be joined by a listed combination of fittings, gaskets, and grooves.

I looked all the way back to NFPA 20 1990 and found a similar wording.  If 
anything, I'd say the OS&Y is typically flanged as its the most common 
configuration to get the valve in, and its typically bolted directly to a 
flanged increaser?  I think this is mostly a "how we've always done it" 
situation.
________________________________
The views, opinions and judgements expressed in this message are solely those 
of the author.  The message contents have not been revewed or approved by S&S
Mike Morey
Project Manager • Fire Protection
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]<mailto:[email protected]>

[cid:[email protected]]





From:        IPA <[email protected]<mailto:[email protected]>>
To:        
[email protected]<mailto:[email protected]>
Date:        12/15/2016 12:32 AM
Subject:        NFPA 20 & Suction Flanges
Sent by:        "Sprinklerforum" 
<[email protected]<mailto:[email protected]>>
________________________________



I might be going crazy but I thought there was a requirement for something in 
the fire pump suction line to have flanged fittings... perhaps the OS&Y? I 
can't find anything like that now that I"m looking for it and I do see a 
general requirement that the fittings can be screwed, flanged or mechanically 
grooved. Is there such a requirement or was there ever one for flanged fittings?

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DgICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=IKmbVraL9UonubDnjpAZI3-cVPX2NSTGwOnmYzfO3io&s=lwe801zss2zRrUfljknUOG87eqj44sYEx5644DrVJHM&e=
This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to