Bill:

I have seen separations of these style    flanges in situations as you describe 
and others.     Personally, I do not spec/use them without rods but there are 
many many out there.

On Dec 16, 2016, at 8:30 AM, 
"[email protected]<mailto:[email protected]>" 
<[email protected]<mailto:[email protected]>> wrote:

Hi Bill,
If you look up the technical data sheet on a "Uniflange" you'll find that this 
device has a rated holding strength in the 25,000 pound range based on the pipe 
diameter. They are commonly used out here in the Wild West. We have never seen 
a failure on a properly installed device.

Mark at Aero
602 820-7894

Sent from my iPhone

On Dec 16, 2016, at 6:20 AM, Bill Brooks 
<[email protected]<mailto:[email protected]>> wrote:

A case came up today about the use of a “mechanical joint wedge action 
restraint” on the suction and discharge side of a diesel driven pump.  Someone 
accepted a change and eliminated the rods, then put a MJWAC at the top of the 
ductile pipe on each side of the pump.  A commissioning agent has refused to 
start the pump based on the concern the restraint will “wiggle” off the end of 
the ductile under repeated pump operation either during the acceptance test or 
sometime later.

Is this a creative use of this type restraint, or is it a totally bad idea?  By 
the way, the underground elbow is a restrained type mechanical joint.

Thanks

Bill Brooks
Brooks Fire Protection Engineering Inc.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to