Good information, do you have any forensic statistics on these failures that 
would give an indication of the cause of the failure? Improper installation, 
rust/corrosion, produce defect?
Mark at Aero
602 820-7894


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Top Myers
Sent: Friday, December 16, 2016 11:44 AM
To: [email protected]
Subject: RE: Use of Set Screw Type Restraint Fire Pump Suction and Discharge

Over the years, we have had a number of Uniflange claims.  Same with some of 
their competitors which are import.  The rating of 25,000 is based on perfect 
conditions and when installed in front of system with water flow upstream the 
water often runs for a long time before noticed. I support Dan Arnolds 
observation.

Top Myers
Myers Risk Services
2102 Kimberton Road, Unit 741
Kimberton, PA 19442
(484) 924-8155   Cell 610-952-0965
[email protected]<mailto:[email protected]>

Providing Solutions For Your Risk Management Needs

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Daniel Arnold
Sent: Friday, December 16, 2016 11:48 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Use of Set Screw Type Restraint Fire Pump Suction and Discharge

Bill:

I have seen separations of these style flanges in situations as you describe 
and others.     Personally, I do not spec/use them without rods but there are 
many, many out there.

(Did not sign my prior post.... Apologies,)

Dan Arnold
Seneca Fire Engineering, LLC



On Dec 16, 2016, at 8:30 AM, 
"[email protected]<mailto:[email protected]>" 
<[email protected]<mailto:[email protected]>> wrote:
Hi Bill,
If you look up the technical data sheet on a "Uniflange" you'll find that this 
device has a rated holding strength in the 25,000 pound range based on the pipe 
diameter. They are commonly used out here in the Wild West. We have never seen 
a failure on a properly installed device.

Mark at Aero
602 820-7894

Sent from my iPhone

On Dec 16, 2016, at 6:20 AM, Bill Brooks 
<[email protected]<mailto:[email protected]>> wrote:
A case came up today about the use of a "mechanical joint wedge action 
restraint" on the suction and discharge side of a diesel driven pump.  Someone 
accepted a change and eliminated the rods, then put a MJWAC at the top of the 
ductile pipe on each side of the pump.  A commissioning agent has refused to 
start the pump based on the concern the restraint will "wiggle" off the end of 
the ductile under repeated pump operation either during the acceptance test or 
sometime later.

Is this a creative use of this type restraint, or is it a totally bad idea?  By 
the way, the underground elbow is a restrained type mechanical joint.

Thanks

Bill Brooks
Brooks Fire Protection Engineering Inc.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to