It is normal for commercial parking garage to be open. The building code 
requires either this or mechanical ventilation to exhaust automobile fumes. 

> On Dec 15, 2016, at 13:58, Steve Leyton <[email protected]> wrote:
> 
> CORRECT, no reduction for QA here.  Instead, please make check for sales tax 
> on larger pipe size payable to Franchise Tax Board, Sacramento CA.
>  
> SL
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Rocci Cetani 3
> Sent: Thursday, December 15, 2016 1:55 PM
> To: [email protected]
> Subject: RE: 13R systems
>  
> 1 large universal parking area 40’x80’,  garage is separated from residential 
> portion by a 1 hour rated wall. (Not a separate building just a 1 hour wall) 
> Sounds like OH1 it is and thanks to the great state of California no area 
> reduction for me. J
>  
> Thanks Steve
>  
> Rocci Cetani III, CET
> Designer
> Water-Based Fire Protections Systems Layout, Nicet Level III
>  
> Northern California Fire Protection Services Inc.
> 16840 Joleen Way Bldg. A
> Morgan Hill, CA 93037
> P-(408) 776-1580 EXT.111
> F-(408) 776-1590
>  
>  
> [email protected]
> www.norcalfire.com
>  
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
> contain confidential information
> belonging to the sender. The information is intended only for the use of 
> individual or entity named above. If you are not the intended recipient, or 
> the employee or agent responsible to deliver this message to the intended 
> recipient, you are hereby notified that any disclosure, copying or taking of 
> any action in reliance on the contents of this information is strictly 
> prohibited. If you have received this transmission in error, please 
> immediately notify us by telephone to arrange for return of the documents.
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Steve Leyton
> Sent: Thursday, December 15, 2016 1:04 PM
> To: [email protected]
> Subject: RE: 13R systems
>  
> First, since carports aren’t addressed in 13R, I think you have to call it a 
> “garage”.   Next, is this one universal parking area or is it 
> compartmentalized into spaces less than 500 sq. ft. (NFPA 13R, 7.2.3.1 and 
> 7.2.4.1)?  Then, are the walls separating it from other compartments rated?  
> 30 minutes?  One-hour?  Or, is there a building separation that would trigger 
> full NFPA 13 (7.3.1)?   Assuming a larger compartment, it’ll probably boil 
> down to OH1 per NFPA 13 with area reduction allowed for QR sprinklers.
>  
> Steve L.
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Rocci Cetani 3
> Sent: Thursday, December 15, 2016 12:54 PM
> To: [email protected]
> Subject: 13R systems
>  
> I have a 3 story apartment building, 1st floor has 4 units and a parking 
> area. 2nd and 3rd floors each have 6 units. The Parking area is on the far 
> end of the building under 2 of the 2nd floor units. The parking area has a 1 
> hr rated wall and door that leads to the 4 units on the 1st floor. In my 
> opinion this isn’t really a garage because it’s completely open on one side, 
> I look at it more as a carport (please correct me if im wrong)…… I believe I 
> should be using section 7.2.2 (13R 2013) where it states  “ the design 
> discharge and design area criteria for area protected by quick response 
> sprinklers shall comply with NFPA 13.”  I’m unsure if this is directing me to 
> calc at OH1 .15/1500 because its automobile parking or if it saying to calc 
> at a .10 over 4 sprinklers  per NFPA 13 11.3 ( not sure this section even 
> applies because 13R 6.4.7 doesn’t say carports fall under the category where 
> residential sprinklers can be used outside dwelling units. I design maybe 2 
> residential projects every year so I’m not as in tune with residential 
> standards as I should be.  Any guidance is much appreciated.
>  
> Thank you!
>  
>  
> Rocci Cetani III, CET
> Designer
> Water-Based Fire Protections Systems Layout, Nicet Level III
>  
> Northern California Fire Protection Services Inc.
> 16840 Joleen Way Bldg. A
> Morgan Hill, CA 93037
> P-(408) 776-1580 EXT.111
> F-(408) 776-1590
>  
>  
> [email protected]
> www.norcalfire.com
>  
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
> contain confidential information
> belonging to the sender. The information is intended only for the use of 
> individual or entity named above. If you are not the intended recipient, or 
> the employee or agent responsible to deliver this message to the intended 
> recipient, you are hereby notified that any disclosure, copying or taking of 
> any action in reliance on the contents of this information is strictly 
> prohibited. If you have received this transmission in error, please 
> immediately notify us by telephone to arrange for return of the documents.
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org