For a twist: Yes, you would follow 3x rule. However, it is likely light hazard 
with ceiling fan. So, since it is non-structural, do you have to follow it? 

I think prudent design is to be the 3x away with QR sprinklers. However, it 
could be ignored since it is non-structural. 

I typically see residential or ex cov sprinklers in these situations and that 
forces you to the 4x rule. Plus the allowance for non-structural is only for 
standard spray sprinklers. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jan 23, 2017, at 2:10 PM, Mark Phillips <[email protected]> wrote:
> 
> NFPA 13 2013 ED 8.6.5.2.1.3 (A)
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Trillium Fire Sprinkler Design Inc.
> Sent: Monday, January 23, 2017 4:06 PM
> To: [email protected]
> Subject: RE: QR STANDARD SPRAY SPRINKLERS
>  
> CAN YOU REFERENCE A CODE FOR ME?
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Mark Phillips
> Sent: January-23-17 4:05 PM
> To: [email protected]
> Subject: RE: QR STANDARD SPRAY SPRINKLERS
>  
> Three times rule applies to the fan housing unit (motor)
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Trillium Fire Sprinkler Design Inc.
> Sent: Monday, January 23, 2017 3:56 PM
> To: [email protected]
> Subject: QR STANDARD SPRAY SPRINKLERS
>  
> I KNOW FOR 13R YOU NEED TO BE A MINIMUM OF 3'-0" AWAY FROM THE CENTER OF A 
> CEILING FAN WITH RESIDENTIAL HEADS
>  
> I CANNOT FIND WHERE THE SAME APPLIES FOR A 13 SYSTEM USING STANDARD Q.R. 
> PENDENT OR CONCEALED HEADS.
>  
> CAN SOMEONE VERIFY OR EDUCATED ME ON THIS PLEASE?
>  
> THANKS
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to