Exactly and well said Mark!

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, February 20, 2017 4:06 PM
To: [email protected]
Subject: RE: K for a Hose Valve

Design it with a computer, measure it with a micrometer, mark it with a piece 
of chalk and cut it with an axe! Sprinkler Design 101!
Mark at Aero
602 820-7894

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Monday, February 20, 2017 3:49 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: K for a Hose Valve


The question still remains as to "why" something like this would be needed.  If 
it just to plug into a computer to make it run calcs, then use Q = k*sqrt(P).

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 2/20/2017 3:37 PM, Brad Casterline wrote:

Nice Allan!

And Steve, if you want 1139 at 100 out the valve you are going to need 143 at 
the standpipe, to get through the nipple and tee. It's like a sprinkler on a 
sprig calc, only the sprinkler is great big and the sprig is short and fat.

Brad
On Feb 19, 2017 6:01 PM, "AKS-Gmail-IMAP" 
<[email protected]<mailto:[email protected]>> wrote:
Lets look at what FM Global has to say. According to FM Global's minimum 
approval standards for these valves, "Approval Standard for Angle and 
Straightaway Hose Valves, Class Number 1521/1522 , December 2014"

"4.11

Friction Loss Test - Traditional Hose Valves Only

1.     4.11.1  Requirement

The valve shall be designed so that the obstruction in the waterway is minimal. 
For valves found to be non- compliant with Sections 3.2.3 and/or 3.2.4, 
friction loss testing is necessary. The valve will be tested in the full open 
position, and the friction loss through the valve will be measured at a flow 
rate that produces a fluid velocity of 20 ft/sec (6.1 m/sec) in Schedule 40 
steel pipe of the same nominal diameter as the valve. The measured friction 
loss shall be less than 10 psi (69 kPa)."
The "sections 3.2.3 and/or 3.2.4" in the text refers to physical seat lift 
dimensions in the valve. So FM does not took at pressure loss if the valve guts 
meet their internal dimension numbers. The standard does not refer to angle 
versus straight in regard to pressure loss. Both patterns must meet the same 
standard. I believe that 20 ft/sec in 2.5" schd. 40 pipe comes to 298 GPM at 10 
psi drop, which comes to a K near 94. Figuring FM approval is "better than your 
average bear.", you might not want to use a K larger than 94. That 94 K would 
lose about 7 psi at 250 gpm.

Allan Seidel
St. Louis, MO


On Feb 19, 2017, at 12:44 PM, Brad Casterline 
<[email protected]<mailto:[email protected]>> wrote:


Of course!
I know this is unorthodox thinking, especially for an NFPA 14 maestro.
But I figured out quite a few years ago how to get not only K, but the Q and P 
that goes with it for a flowing outlet with only two pieces of information; the 
nominal diameter and the coefficient of discharge.
And after the twists and turns and showing off and stepping in it this weekend 
I wanted to take my best shot at being the anybody with a decent K for a 2.5 
inch hose valve, as Vince asked.
So "In the same way as a nominal 1/2" sprinkler..."
K=113.85, if the C of D is .61,
final answer.

Thanks for hollering back, I was getting lonely out here,

Brad
On Feb 19, 2017 11:13 AM, "Steve Leyton" 
<[email protected]<mailto:[email protected]>> wrote:
Of course, that should have been GPM and not PSI.


Steve


-------- Original message --------
From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Date: 2/19/17 8:44 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>,
 Vince Sabolik <[email protected]<mailto:[email protected]>>
Subject: RE: K for a  Hose Valve

Awesome. So the "nominal" flow at 100 PSI will be 1,138.5 PSI?

Maybe we need to change the hydraulic design method in the standard.

Steve L.


-------- Original message --------
From: Brad Casterline <[email protected]<mailto:[email protected]>>
Date: 2/19/17 2:09 AM (GMT-08:00)
To: Vince Sabolik <[email protected]<mailto:[email protected]>>, 
[email protected]<mailto:[email protected]>
Subject: Re: K for a 2½" Hose Valve


K=113.85

In the same way that a nominal 1/2" sprinkler with a Coefficient of Discharge 
of .75 has a K=5.6, a nominal 2.5" hose valve with a Coefficient of Discharge 
of .61 has a K=113.85.

Brad
On Feb 17, 2017 8:28 AM, "Vince Sabolik" 
<[email protected]<mailto:[email protected]>> wrote:
Good morning, everyone...

Does anybody have a decent K Factor for a 2½" hose valve?

Thanks!      Vince
<20914 x WTFP Logo NEW1.jpg>
11351 Pearl Road /  Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800<tel:%28440%29%20238-4800> Fax 440 
238-4876<tel:%28440%29%20238-4876> Cell 440 724-7601<tel:%28440%29%20724-7601>

Vince Sabolik

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to