The interesting thing, is that I would say 99.99% of the ones I deal
with are awesome. There is just the 0.01% that cause headaches.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 5/8/2017 9:31 AM, Matthew J Willis wrote:
You’re just a magnet for fun with AHJ’s!
*/Matthew J. Willis/**//*
*/Project Manager/*
*/Rapid Fire Protection Inc./* <http://rapidfireinc.com/>
*/1530 Samco Road/*
*/Rapid City, SD 57702/*
*/Office-605.348.2342/*
*/Direct Line-605.593.5063/*
*/Cell-605.391.2733/*
*/Fax:-605.348.0108/*
cid:[email protected]
*From:*Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*Travis Mack, SET
*Sent:* Monday, May 8, 2017 10:30 AM
*To:* [email protected]
*Subject:* Re: special inspections
In this project, it was shown on the architectural plans. Quite
clearly called out.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected] <mailto:email:[email protected]>
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via:https://www.hightail.com/u/MFPDesign
LinkedIn:https://www.linkedin.com/in/travismack
On 5/8/2017 9:28 AM, John Drucker wrote:
Ahhh I was waiting for that question. Because it's in the
sprinkler standard, noted on the sprinkler plans by the sprinkler
designer, and often the architect nor engineer know the sprinkler
designer took that option, or it conflicts with the architects design.
As a result we deny such applications unless the insulation fill
is also shown on the architectural plans. In New Jersey it is also
an adopted regulation that any plans, shop drawings etc prepared
by other than the principal designer have to be reviewed and
approved by the principal designer with an accompanying letter at
the time of submission to that affect. Often enough we get back
from the principal designer that the method submitted by others is
not approved.
On May 8, 2017 12:14 PM, "rongreenman ." <[email protected]>
<mailto:[email protected]> wrote:
Seems to me that if the architect or GC wants to fill the space
with insulation instead of sprinkle ring it's between him and the
insulator to get it right. If the AHJ wants to get involved then
OK, but with them. If you don't put in sprinklers because
insulation has been approved what business is it of the sprinkler guy?
On Mon, May 8, 2017 at 10:54 AM John Drucker - Home
<[email protected] <mailto:[email protected]>> wrote:
Members,
When an interstitial space is filled entirely with
non-combustible insulation we coordinate with the contractor
and perform the inspection ourselves.
John
John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Electrical Subcode Official
Building Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected] <mailto:[email protected]>
Cell/Text: 732-904-6823
_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
------------------------------------------------------------------------
AVG logo <http://www.avg.com/internet-security>
This email has been checked for viruses by AVG antivirus software.
www.avg.com <http://www.avg.com/internet-security>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
---
This email has been checked for viruses by AVG.
http://www.avg.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org