One of our local AHJ's observed that there are UL listed assemblies for floor 
ceiling assemblies and that the addition of insulation in fact voids the 
listing of some that aren't insulated (remember, this is sunny CA).    So for 
plans submitted to that particular agency, we not only have to pick between the 
3,000 sq. ft. (or 8-sprinkler) design area or using insulation.  In the case of 
the latter, they want a detail of the floor-ceiling and/or roof-ceiling 
assembly showing the insulation AND the UL listing number for the assembly.   
On the sprinkler plans.

At first, we were frustrated because they hadn't codified this and we were just 
getting back plan review comments.  But I see why they're doing it and I agree 
with this practice.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Drucker
Sent: Monday, May 08, 2017 9:29 AM
To: [email protected]
Subject: Re: special inspections

Ahhh I was waiting for that question. Because it's in the sprinkler standard, 
noted on the sprinkler plans by the sprinkler designer, and often the architect 
nor engineer know the sprinkler designer took that option, or it conflicts with 
the architects design.

As a result we deny such applications unless the insulation fill is also shown 
on the architectural plans. In New Jersey it is also an adopted regulation that 
any plans, shop drawings etc prepared by other than the principal designer have 
to be reviewed and approved by the principal designer with an accompanying 
letter at the time of submission to that affect. Often enough we get back from 
the principal designer that the method submitted by others is not approved.
On May 8, 2017 12:14 PM, "rongreenman ." 
<[email protected]<mailto:[email protected]>> wrote:
Seems to me that if the architect or GC wants to fill the space with insulation 
instead of sprinkle ring it's between him and the insulator to get it right. If 
the AHJ wants to get involved then OK, but with them. If you don't put in 
sprinklers because insulation has been approved what business is it of the 
sprinkler guy?
On Mon, May 8, 2017 at 10:54 AM John Drucker - Home 
<[email protected]<mailto:[email protected]>> wrote:
Members,

When an interstitial space is filled entirely with non-combustible insulation 
we coordinate with the contractor and perform the inspection ourselves.

John

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Electrical Subcode Official
Building Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]<mailto:[email protected]>
Cell/Text: 732-904-6823




_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to