You might want to look at FM Data Sheet 1-23. They have scheme for protection 
of wall openings via water spray nozzles protecting both sides of the wall, 
using separate deluge systems.

Larry Keeping

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Micah Davis, SET
Sent: May-18-17 8:25 AM
To: [email protected]
Subject: Re: Water curtain for wall opening


Todd

I ran into a similar situation at a large food packaging plant.  The protection 
we finally decided on was a small deluge system with heat detectors on both 
sides of the wall.  The heat detectors could be mounted at the ceiling where 
the heat would gather.



Micah Davis

www.dynamicfiredesigns.com<http://www.dynamicfiredesigns.com>



________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, May 18, 2017 6:53 AM
To: Sprinkler Forum
Subject: Water curtain for wall opening

I have been asked to look at a situation in an industrial occupancy where there 
are two garage -door size horizontal openings in a wall. The openings cannot 
realistically be closed, so they are asking about a water curtain. I have a 
couple of questions: First, NFPA 13 discusses water curtains around vertical 
openings but not horizontal, from what i found. Am i missing something?
Second, the ceiling is approximately 12 ft above the top of the openings. The 
sprinklers need to be 12" from the deck max. Will that vertical distance create 
an issue with the water curtain performance.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)