Have a look at Factory Mutual Datasheet 1-23 Fire Barriers and Protection of 
Openings

 

Russell Gregory

Christchurch 

New Zealand

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, 18 May 2017 11:54 PM
To: Sprinkler Forum
Subject: Water curtain for wall opening

 

I have been asked to look at a situation in an industrial occupancy where there 
are two garage -door size horizontal openings in a wall. The openings cannot 
realistically be closed, so they are asking about a water curtain. I have a 
couple of questions: First, NFPA 13 discusses water curtains around vertical 
openings but not horizontal, from what i found. Am i missing something?

Second, the ceiling is approximately 12 ft above the top of the openings. The 
sprinklers need to be 12" from the deck max. Will that vertical distance create 
an issue with the water curtain performance.


Todd G Williams, PE