I don't know what the specific conditions are of this application, but that 
statement is not accurate. We have done several projects where apartments are 
two-story and there is only access on alternate floors. Believe me, every 
stairwell in most buildings is a required stair.


Steve


-------- Original message --------
From: Jeff Normand <[email protected]>
Date: 5/22/17 5:21 PM (GMT-05:00)
To: [email protected], [email protected]
Subject: Re: Hose Valve Location

I'm thinking it says a hose valve at every required stairwell. Since this stair 
does not have access then it would not be a required stairway. Therefore hose 
valve not required.

I have run into this before on a high rise with 3 stairs on the lower 8 levels 
and 2 stairs on upper levels. One of the stairs did not have access on the 
lower 8 floors, therefore no hose valve.

Jeff

On Mon, May 22, 2017 at 12:50 PM, Bob 
<[email protected]<mailto:[email protected]>> wrote:
I have a stairway that has no access to the 1st floor, but it does exit to the 
outside of building.
The ANNEX material shows a hose valve located with respect to the floor access, 
since there is no floor access would the hose valve be required for this level?

Thank you,

Bob Knight, CET III
208-318-3057