Where does that note come from?  The AHJ or owner or Engineer of Record?

Either way that info should be provided by the Engineer of Record to the 
installing contractor to be included in submittals to the AHJ.  I would 
certainly hope an Engineer is not dumping this off on the installing contractor.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Wednesday, May 31, 2017 2:34 PM
To: [email protected]
Subject: Grow Facilities [EXTERNAL]


This is obviously outside of our scope and I am punting this back up the chain. 
 But, has anyone that is sprinklering these MJ facilties run into this:

"Provide a letter from a state licensed PE or Consulting Firm approved by the 
City of XXXXXXX, that supports the fire sprinkler design assumptions.  The 
letter shall be signed (wet) and address the design assumptions that includes 
the use of CO2 enrichment, flammable liquids/gasses, and hazardous waste and 
the impact that includes the overall Heat Release Rate (HRR) and the ability of 
the fire sprinkler system to suppress a fire. Reference 2016 state fire code 
section xxx.x.x"

I used xxx to block out any reference to the particular project.

Any ideas on this stuff.  We were hired to just design the system per OH2.  
This is going to get interesting.

--

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack

[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-green-avg-v1.png]<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>

Virus-free. 
www.avg.com<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to