That note comes from the plan reviewer. My firm was hired to design to
OH2. But it got rejected by the AHJ and had that note on the
rejection. My scope was well defined and this is way out of the scope.
So I was just wondering what others have encountered in these facilities.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 5/31/2017 12:49 PM, Prahl, Craig/GVL wrote:
Where does that note come from?The AHJ or owner or Engineer of Record?
Either way that info should be provided by the Engineer of Record to
the installing contractor to be included in submittals to the AHJ.I
would certainly hope an Engineer is not dumping this off on the
installing contractor.
*Craig L. Prahl**
*Fire Protection Group Lead/SME
*CH2M*
200 Verdae Blvd.
Greenville, SC 29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension77540
[email protected]
*From:*Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*Travis Mack, SET
*Sent:* Wednesday, May 31, 2017 2:34 PM
*To:* [email protected]
*Subject:* Grow Facilities [EXTERNAL]
This is obviously outside of our scope and I am punting this back up
the chain. But, has anyone that is sprinklering these MJ facilties
run into this:
"Provide a letter from a state licensed PE or Consulting Firm approved
by the City of XXXXXXX, that supports the fire sprinkler design
assumptions. The letter shall be signed (wet) and address the design
assumptions that includes the use of CO2 enrichment, flammable
liquids/gasses, and hazardous waste and the impact that includes the
overall Heat Release Rate (HRR) and the ability of the fire sprinkler
system to suppress a fire. Reference 2016 state fire code section xxx.x.x"
I used xxx to block out any reference to the particular project.
Any ideas on this stuff. We were hired to just design the system per
OH2. This is going to get interesting.
--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected] <mailto:email:[email protected]>
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via:https://www.hightail.com/u/MFPDesign
LinkedIn:https://www.linkedin.com/in/travismack
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
Virus-free. www.avg.com
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
---
This email has been checked for viruses by AVG.
http://www.avg.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org