Travis,

Didn't they just change the IBC to allow that?


Design Mgr
*Living Water Fire Protection, LLC*
1160 McKenzie Rd.
Cantonment, FL 32533
(850) 937-1850


On Tue, Jun 6, 2017 at 10:04 AM, Travis Mack <[email protected]> wrote:

> You can not have a 13 system with 13R in the units. The system is either
> designed per 13 or 13R, not a hybrid.
>
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-
> LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>
> Sent from my iPhone
>
> On Jun 6, 2017, at 8:01 AM, Brian Harris <[email protected]>
> wrote:
>
> It’s (4) stories, the notes on the FP drawings call for a 13 system with
> 13R coverage in the guest room.
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssytemsinc.com <http://bvssystemsinc.com/>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Trillium
> Fire Sprinkler Design Inc.
> *Sent:* Tuesday, June 06, 2017 10:40 AM
> *To:* [email protected]
> *Subject:* RE: Hotels
>
>
>
> I do several of these every year.
>
>
>
> How tall are you talking.
>
>
>
> Are they wanting 13 or 13R?
>
>
>
> This determines a few starting factors
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Brian
> Harris
> *Sent:* June-06-17 10:37 AM
> *To:* [email protected]
> *Subject:* Hotels
>
>
>
> Been doing this sprinkler stuff for just over 11 years now and finally ran
> into my first hotel project. Any tips/pointers from you guys that do a lot
> of these ?
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> Design Manager
>
> bvssystemsinc.com
>
> Phone: 704.896.9989 <(704)%20896-9989>
>
> Fax: 704.896.1935 <(704)%20896-1935>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org