It sounds like similar situations we have seen and we have had to sprinkler
old and new areas, since they were connected.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Thomas Reinhardt
Sent: Thursday, June 8, 2017 11:59 AM
To: [email protected]
Subject: FW: Do they need sprinklers?

 

 

 

From: Thomas Reinhardt 
Sent: Thursday, June 08, 2017 10:53 AM
To: '[email protected]'
Subject: Do they need sprinklers?

 

I have a place of religious worship(A3) not sprinklered. They want to open
up an elementary school in the basement(below grade) which has currently
multiple rooms. Ages of children five through thirteen. We use IFC and IBC
2012 edition. The occupancy for the school I believe would be Education,
thus Accessory to place of worship as defined in the IFC. If occupant load
is less than 100 it shall be classified as an A3. Chapter 9 section
903.2.1.3(Fire Protection) relates that the fire area is located on a floor
other than level of exit discharge it must be sprinklered. Also group E
(903.2.3) say the same. I contend that they must not only sprinkler the
basement, but also the entire building as interpreted in NFPA(2010 edition)
chapter 4 section 4.1. Sorry so long . Any comments would be appreciated. 