Does the state modify the IBC/IFC when they adopt the model code? Sections 
around schools are a favorite to have state amendments.

Best,

Bruce Verhei 

> On Jun 8, 2017, at 09:51, Roland Huggins <[email protected]> wrote:
> 
> Treating this as a new or up to current code issue, the building code does 
> allow only portions of a building to be sprinklered.  It all depends on the 
> occupancy, location etc.
> 
> 405.3 Automatic sprinkler system. The highest level of exit discharge serving 
> the underground portions of the building and all levels below shall be 
> equipped with an automatic sprinkler system 
> 
> 
> The A-3 requires just that floor and all stories between it and the level of 
> exit discharge to be sprinklered
> 
> A such, unless there is an occupancy that says sprinklers must be throughout 
> the building verse just that pertinent floor or fire area (like stated for 
> Group R), then the NFPA 13 criteria for throughout is irrelevant (being 
> superseded by the code).  Keep in mind that 13 came out of the Insurance 
> business and things like business continuity is an inherit part of OUR 
> philosophy and drives such text in NFPA 13.  Unfortunately the codes allow 
> those decisions (to some degree) to be driven by the owner and the EOR.  This 
> is just starting to be acknowledged by NFPA 13 as shown by the below new 
> commentary in the Sprinkler Handbook (which I knew was there since guess who 
> wrote it?). 
> 
> 
> 4.1 Level of Protection
> 
> A building, where protected by an automatic sprinkler system installation, 
> shall be provided with sprinklers in all areas except where specific sections 
> of this standard permit the omission of sprinklers.
> 
> The oldest and most important design rule of NFPA 13 is that sprinklers 
> should be installed in all areas of a building. This requirement dates back 
> to the first edition of NFPA 13, published in 1896, which contained the 
> statement “sprinklers to be placed throughout premises” in the section on 
> location and arrangement of sprinklers. This philosophy is part of the 
> insurance-based attitude toward risk and levels of protection that founded 
> the standard. To truly minimize risk, the entire building must be protected.  
> However, insurance is no longer the primary driver for when sprinkler 
> protection is provided. That role is played by the building codes. It is 
> possible to have a mixed occupancy building that is fully compliant with the 
> building code and only have one of the occupancies sprinklered. When this 
> occurs, it should not be viewed as a limited area system, and NFPA 13 should 
> be applied in its entirety throughout the portion of the building containing 
> the protected occupancy. 
> 
> 
> Roland
> 
> Roland Huggins, PE - Senior VP Engineering
> American Fire Sprinkler Assn.    
> Dallas, TX
> http://www.firesprinkler.org
> 
> Fire Sprinklers Saves Lives
> 
> 
> 
> 
>> On Jun 8, 2017, at 8:59 AM, Thomas Reinhardt <[email protected]> 
>> wrote:
>> 
>>  
>>  
>> From: Thomas Reinhardt 
>> Sent: Thursday, June 08, 2017 10:53 AM
>> To: '[email protected]'
>> Subject: Do they need sprinklers?
>>  
>> I have a place of religious worship(A3) not sprinklered. They want to open 
>> up an elementary school in the basement(below grade) which has currently 
>> multiple rooms. Ages of children five through thirteen. We use IFC and IBC 
>> 2012 edition. The occupancy for the school I believe would be Education, 
>> thus Accessory to place of worship as defined in the IFC. If occupant load 
>> is less than 100 it shall be classified as an A3. Chapter 9 section 
>> 903.2.1.3(Fire Protection) relates that the fire area is located on a floor 
>> other than level of exit discharge it must be sprinklered. Also group E 
>> (903.2.3) say the same. I contend that they must not only sprinkler the 
>> basement, but also the entire building as interpreted in NFPA(2010 edition) 
>> chapter 4 section 4.1. Sorry so long . Any comments would be appreciated. 
>> Tom Reinhardt
>> Fire Inspector/Plan Reviewer
>> Skokie Fire Department
>> 7424 Niles Center Road
>> Skokie, IL 60077
>> Office: 847-982-5342
>> [email protected]
>>  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to