If the packaging materials are class 3 commodities, they could design to FM.

Matt


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 4:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Heating cable and 1" wrap.

What about using Single Interlock Pre-action.

We got a bid for a "Quell" pre-action dry system with detection that is crazy 
expensive with a 2500 gpm fire pump.
Good city water is adequate for an ESFR system without a pump from a 20" water 
main.

What is the poor reliability aspect Concern?

Art

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Prahl, Craig/GVL
Sent: Tuesday, June 13, 2017 5:17 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Heating cable and 1" wrap.

?  You could use heat detection in lieu of smoke detection depending on 
environmental conditions.

Heat tracing a complete system is a disaster waiting to happen IMHO.

Also the Heat trace system must be electronically supervised to insure 
operability.  So he will need a fire alarm system for it to connect to.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 4:58 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Heating cable and 1" wrap. [EXTERNAL]

I have a client that is renovating an uninsulated 30,000 SF shed warehouse.
He does not want to heat the building.

Dry system requirements for solid piled storage over 25Ft high in 35 Ft. high 
building are not available.

I am pushing for an ESFR wet system in a heated building.
Rather than heating an uninsulated building owner suggests we heat the 
sprinkler pipe with heat cable and 1" insulation.
This method is in 13. Tyco has a system to apply heating cable to branch lines 
and cross mains.

In over 50 years I have never seen or heard of heat tracing being done. I think 
it is a mistake due to reliability and cost
There must be reasons this heating method is not being installed on a sprinkler 
system.

What arguments can I use to avoid this method of keeping a wet grid system from 
freezing.



Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell


[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>

Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to