For a space with such a small volume as 1280 cubic feet I think the
simplest and most effective would be a stand alone clean agent suppression
system (FM-200/Novec 1230). Besides superior extinguishing capabilities, it
will have no negative effects on the equipment being stored/tested there,
should the system deploy. You would need a small fire alarm panel, a couple
detectors/pull station, and a small area to house the tank.
Hope this helps, but feel free to reach out if you have any questions.

Regards,
Wayne T. Cordiner Jr.
917-426-5844
[email protected]

On Tue, Jul 18, 2017 at 3:23 PM, James Crawford <[email protected]>
wrote:

> We have someone that has a 20’ x 8’ x8’ metal shipping container in their
> warehouse that they use to test lithium batteries, the AHJ want them to
> sprinkler this space, but the application of water to the batteries is not
> the best solution.
>
>
>
> Any ideas out there?
>
>
>
>
>