James, For a space with such a small volume as 1280 cubic feet I think the simplest and most effective would be a stand alone clean agent suppression system (FM-200/Novec 1230). Besides superior extinguishing capabilities, it will have no negative effects on the equipment being stored/tested there, should the system deploy. You would need a small fire alarm panel, a couple detectors/pull station, and a small area to house the tank. Hope this helps, but feel free to reach out if you have any questions.
Regards, Wayne T. Cordiner Jr. 917-426-5844 [email protected] On Tue, Jul 18, 2017 at 3:23 PM, James Crawford <[email protected]> wrote: > We have someone that has a 20’ x 8’ x8’ metal shipping container in their > warehouse that they use to test lithium batteries, the AHJ want them to > sprinkler this space, but the application of water to the batteries is not > the best solution. > > > > Any ideas out there? > > > > > > Thank you > > > > > > James Crawford > > Phaser Fire Protection Ltd. > > Phone 604-888-0318 <(604)%20888-0318> > > Fax 604-888-4732 <(604)%20888-4732> > > Cel 604-790-0938 <(604)%20790-0938> > > Email [email protected] > > Web www.phaserfire.ca > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >