Chapter 8 applies ONLY to ceiling sprinklers. There are obstruction rules for 
in-rack sprinklers in chapter 16 and 17.  There are only three aspects:  
clearance above the load, distance from uprights, and clearance below the 
horizontal rack members.  The interesting part is that when they apply is 
affected by the type of sprinkler, the commodity classification, the type of 
rack, and the height of storage.    Although we have the 25 ft storage height 
firmly ingrained in our brains, 20 ft is the magical number for in-rack 
obstructions. 

Roland


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Jul 26, 2017, at 10:39 AM, Dan Arbel <[email protected]> wrote:
> 
> Dear All
>  
> The NFPA 13 contains a great deal of obstruction rules in chapter 8. 
>  
> There is no mention of obstructions in the chapters relating to In-Rack. 
>  
> In a major warehouse I found all in rack sprinklers installed upright between 
> the racks beams violating the obstruction rules of chapter 8  (As well as of 
> the specific FMglobal instructions for in-racks).
>  
> The designer argues that there are no rules of sprinkler positioning between 
> the racks and that the most important factor is to prevent damage to the 
> sprinkler. 
>  
> Would appreciate your opinions. 
>  
> Dan  
>  
>  
>  
> Dan Arbel Risk Engineering
> T: 972-4-8243337
> F: 972-4-8243278
> M: 972-52-6611337
> Mail: [email protected] <mailto:[email protected]>
> W: www.riskmanage.com <http://www.riskmanage.com/>
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to