Chapter 8 applies ONLY to ceiling sprinklers. There are obstruction rules for in-rack sprinklers in chapter 16 and 17. There are only three aspects: clearance above the load, distance from uprights, and clearance below the horizontal rack members. The interesting part is that when they apply is affected by the type of sprinkler, the commodity classification, the type of rack, and the height of storage. Although we have the 25 ft storage height firmly ingrained in our brains, 20 ft is the magical number for in-rack obstructions.
Roland Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> Fire Sprinklers Saves Lives > On Jul 26, 2017, at 10:39 AM, Dan Arbel <[email protected]> wrote: > > Dear All > > The NFPA 13 contains a great deal of obstruction rules in chapter 8. > > There is no mention of obstructions in the chapters relating to In-Rack. > > In a major warehouse I found all in rack sprinklers installed upright between > the racks beams violating the obstruction rules of chapter 8 (As well as of > the specific FMglobal instructions for in-racks). > > The designer argues that there are no rules of sprinkler positioning between > the racks and that the most important factor is to prevent damage to the > sprinkler. > > Would appreciate your opinions. > > Dan > > > > Dan Arbel Risk Engineering > T: 972-4-8243337 > F: 972-4-8243278 > M: 972-52-6611337 > Mail: [email protected] <mailto:[email protected]> > W: www.riskmanage.com <http://www.riskmanage.com/> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org