Roland,

 

You are right about Chapter 8.   So much details.

 

The handling in the code of the In-Rack obstruction problem, which is not
less important than the ceiling problem, leads to  severely obstructed
In-racks  installations. 

 

I observed it several times.  

 

The FMglobal instructions are very clear. 

 

Dan

 

Dan Arbel Risk Engineering

T: 972-4-8243337

F: 972-4-8243278

M: 972-52-6611337

Mail:  <mailto:[email protected]> [email protected]

W: www.riskmanage.com

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Wednesday, July 26, 2017 10:09 PM
To: [email protected]
Subject: Re: Positioning od sprinklers between the racks beams.

 

Chapter 8 applies ONLY to ceiling sprinklers. There are obstruction rules
for in-rack sprinklers in chapter 16 and 17.  There are only three aspects:
clearance above the load, distance from uprights, and clearance below the
horizontal rack members.  The interesting part is that when they apply is
affected by the type of sprinkler, the commodity classification, the type of
rack, and the height of storage.    Although we have the 25 ft storage
height firmly ingrained in our brains, 20 ft is the magical number for
in-rack obstructions. 

 

Roland

 

 

Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.    

Dallas, TX

http://www.firesprinkler.org <http://www.firesprinkler.org/> 

 

Fire Sprinklers Saves Lives

 

 

 

On Jul 26, 2017, at 10:39 AM, Dan Arbel <[email protected]
<mailto:[email protected]> > wrote:

 

Dear All

 

The NFPA 13 contains a great deal of obstruction rules in chapter 8. 

 

There is no mention of obstructions in the chapters relating to In-Rack. 

 

In a major warehouse I found all in rack sprinklers installed upright
between the racks beams violating the obstruction rules of chapter 8  (As
well as of the specific FMglobal instructions for in-racks).

 

The designer argues that there are no rules of sprinkler positioning between
the racks and that the most important factor is to prevent damage to the
sprinkler. 

 

Would appreciate your opinions. 

 

Dan  

 

 

 

Dan Arbel Risk Engineering

T: 972-4-8243337

F: 972-4-8243278

M: 972-52-6611337

Mail:  <mailto:[email protected]> [email protected]

W:  <http://www.riskmanage.com/> www.riskmanage.com

 

_______________________________________________
Sprinklerforum mailing list
 <mailto:[email protected]>
[email protected]
 
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to