Right. Basically, if you're flowing an attack stream from the SP, you don't need the sprinklers. If the sprinklers are working, you don't need attack stream from the SP. Inside hose allowance is for hose connections to sprinkler systems, which by definition are not standpipes. Where you need to add the HSA is if you have a common water supply to hydrants and the system in question, i.e. outside hose. This is all pretty well spelled out in NFPA 13, 2016 ed., §11.1.6.3.1 and §11.1.6.4.
SML From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, August 30, 2017 3:54 PM To: [email protected] Subject: RE: NFPA 13 8.17.5.2.2(1) Aren't they treated as separate calculations. Just as site fire flow is not added to the fire sprinkler system. That is how I was taught. Actually, I think it was Steve L that beat that into my head long ago. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Wednesday, August 30, 2017 3:52 PM To: [email protected]<mailto:[email protected]> Subject: RE: NFPA 13 8.17.5.2.2(1) Roland? Ray Lambert are you out there? This is a LONG-simmering topic of discussion the AFSA tech dept. and also the NFPA community. Short answer is NO, you do not have to include any HSA for standpipe connections. My opinion only (after Roland branded it on my a**). Steve L. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Kyle.Montgomery Sent: Wednesday, August 30, 2017 3:36 PM To: [email protected]<mailto:[email protected]> Subject: RE: NFPA 13 8.17.5.2.2(1) I'm wondering why it isn't more common, considering you purchase about half as many PRVs that way. Would you need to flow a hose allowance through that valve as part of you sprinkler calculation? From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Wednesday, August 30, 2017 3:21 PM To: [email protected]<mailto:[email protected]> Subject: [EXTERNAL] RE: NFPA 13 8.17.5.2.2(1) It's not the most common arrangement but a common pressure reducing valve on the supply side of the floor control and hose connection for a combined standpipe is acceptable so long as it all works hydraulically. The foregoing is my opinion only and is not intended to represent the NFPA 14 Technical Committee, nor serve as an interpretation of the standard. Steve Leyton Protection Design & Consulting San Diego, CA From: Sprinklerforum [mailto:[email protected]] On Behalf Of Kyle.Montgomery Sent: Wednesday, August 30, 2017 3:19 PM To: [email protected]<mailto:[email protected]> Subject: RE: NFPA 13 8.17.5.2.2(1) Not to sidetrack this thread... but is the arrangement Colin is describing acceptable? I have never found anything in the code saying it isn't, but I would say that almost every installation I've seen has a separate pressure-reducing hose valve and pressure-reducing system control valve... which is obviously more expensive. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Colin Carew (Cambridge) Sent: Wednesday, August 30, 2017 2:10 PM To: [email protected]<mailto:[email protected]> Subject: [EXTERNAL] NFPA 13 8.17.5.2.2(1) Wondering , what is reason behind the Control valve and check valve of the same size at the connection is required per 13 8.17.5.2.2 (1) I have a connection , where I connect to the standpipe with 2.5" pipe and then to a PRV control valve , then after I feed a standard hose valve and reduce down to 2" for my sprinkler control valve assembly . Thanks . Colin Carew
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org