But what is everyone's opinion on the control assembly for the sprinkler feed 
being the same size ( 2.5" Hose valve )

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: August-31-17 1:20 PM
To: [email protected]
Subject: RE: NFPA 13 8.17.5.2.2(1)

The figures that are shown for this section [A.8.17.5.2.2(a) and (b)] show your 
classic combination standpipe, though. That's what is confusing me. I've always 
thought of "inside hose" or "hose connections supplied by a sprinkler system" 
as being differentiated from standpipe connections because they are DOWNSTREAM 
of the system control valve (is that correct?). It seems like the handbook is 
saying you need to add a hose allowance (like 50 or 100 GPM) at the hose valve 
connection for this scenario (classic combo standpipe shown in figure) as well 
as for small "inside" hose connections.

What am I missing?

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Thursday, August 31, 2017 9:22 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Re: NFPA 13 8.17.5.2.2(1)

Yes, for hose connections that are supplied by a sprinkler system. Adding the 
flow at the available pressure makes get an allowance as opposed to having to 
balance the flows and pressures the way you would for added rack demand.  
However, hose connections supplied by a sprinkler system are most assuredly not 
standpipes.

My opinion only ...

Steve


-------- Original message --------
From: "Kyle.Montgomery" 
<[email protected]<mailto:[email protected]>>
Date: 8/31/17 8:21 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: RE: NFPA 13 8.17.5.2.2(1)

I read the handbook commentary for 8.17.5.2, and now I'm confused again:

"When either one of the hose connections described in 8.17.5 is provided, the 
flow rates need only be added to the sprinkler system at the design pressure 
available at the point of connection to the sprinkler system pipe."

Is this not referring to a hose stream allowance?

Also, can anyone comment on Colin's original question? (Sorry for hi-jacking 
your thread)

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Wednesday, August 30, 2017 4:19 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: NFPA 13 8.17.5.2.2(1)

This has been my understanding as well. I wonder why more people don't do it 
this way?

I've done it myself one time. But usually am met with a lot of skepticism in 
the form of "well, if this is acceptable, why doesn't everyone do it that way?"

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, August 30, 2017 4:01 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: NFPA 13 8.17.5.2.2(1)

Right.  Basically, if you're flowing an attack stream from the SP, you don't 
need the sprinklers.  If the sprinklers are working, you don't need attack 
stream from the SP.   Inside hose allowance is for hose connections to 
sprinkler systems, which by definition are not standpipes.  Where you need to 
add the HSA is if you have a common water supply to hydrants and the system in 
question, i.e. outside hose.   This is all pretty well spelled out in NFPA 13, 
2016 ed., §11.1.6.3.1 and §11.1.6.4.

SML

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>
Sent: Wednesday, August 30, 2017 3:54 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: NFPA 13 8.17.5.2.2(1)

Aren't they treated as separate calculations.  Just as site fire flow is not 
added to the fire sprinkler system.  That is how I was taught.  Actually, I 
think it was Steve L that beat that into my head long ago.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, August 30, 2017 3:52 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: NFPA 13 8.17.5.2.2(1)

Roland?   Ray Lambert are you out there?

This is a LONG-simmering topic of discussion the AFSA tech dept. and also the 
NFPA community.   Short answer is NO, you do not have to include any HSA for 
standpipe connections.

My opinion only (after Roland branded it on my a**).

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Wednesday, August 30, 2017 3:36 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: NFPA 13 8.17.5.2.2(1)

I'm wondering why it isn't more common, considering you purchase about half as 
many PRVs that way.

Would you need to flow a hose allowance through that valve as part of you 
sprinkler calculation?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, August 30, 2017 3:21 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: NFPA 13 8.17.5.2.2(1)

It's not the most common arrangement but a common pressure reducing valve on 
the supply side of the floor control and hose connection for a combined 
standpipe is acceptable so long as it all works hydraulically.

The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA






From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Wednesday, August 30, 2017 3:19 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: NFPA 13 8.17.5.2.2(1)

Not to sidetrack this thread... but is the arrangement Colin is describing 
acceptable? I have never found anything in the code saying it isn't, but I 
would say that almost every installation I've seen has a separate 
pressure-reducing hose valve and pressure-reducing system control valve... 
which is obviously more expensive.


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Colin Carew (Cambridge)
Sent: Wednesday, August 30, 2017 2:10 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] NFPA 13 8.17.5.2.2(1)


Wondering ,  what is reason behind the Control valve and check valve of the 
same size at the connection is required per 13 8.17.5.2.2 (1)


I have a connection , where I connect to the standpipe  with 2.5" pipe and then 
 to a PRV control valve , then after I feed a standard hose valve and reduce 
down to 2" for my sprinkler control valve assembly .


Thanks .


Colin Carew