Read 7.2.4 closely:  “Where more than two hose connections are used downstream 
of a pressure-regulating device …”

A floor control assembly or a single hose connection with integral PR device 
does not require redundancy or a bypass because that section of the standard 
only applies to multiple hose connections influenced by a single PR device.

My opinion only, but the standard clearly says what is says …

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Silva
Sent: Wednesday, September 06, 2017 11:27 AM
To: [email protected]
Subject: PRV By-pass

NFPA 14, 2010, 7.2.4 (4) requires a bypass across a prv. Is it only when 
multiple smaller prv's are used instead of a larger prv, or whenever any prv is 
used?
My application is there is a prv at the floor control stations supplying 
combined sprinkler/standpipe. Would this prv need a by-pass?
The other question is will every prv need control valves upstream and 
downstream?
I know it is good engineering practice to have the valves and by-pass, but very 
often there is not much space inside the stairs. What is the general industry 
practice?
Thanks,
Tony