Thanks Don – yes, my ref is to current edition.  But the intent is that only 
when multiple hose connections are influence is it required to furnish 
redundancy, which begets the bypass.

SML

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Don Casey
Sent: Wednesday, September 06, 2017 12:01 PM
To: [email protected]
Subject: RE: PRV By-pass

Steve is referencing the 2013 and / or the 2016 editions of the standard.  
Regardless, look at Item (3) which specifically addresses scenarios when two 
hose connections are downstream of a PRV.

Cheers
Don


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Silva
Sent: 2017/09/06 2:45 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: PRV By-pass

7.2.4 in entirety is as follows:

7.2.4* When system pressure-regulating devices are used in lieu
of providing separate pumps, multiple zones shall be permitted
to be supplied by a single pump and pressure-regulating device(
s) under the following conditions:
(1) Pressure-regulating device(s) shall be permitted to control
pressure in the lower zone(s).
(2) A method to isolate the pressure-regulating device(s)
shall be provided for maintenance and repair.
(3) Regulating devices shall be arranged so that the failure of
any single device does not allow pressure in excess of
175 psi (12.1 bar) to more than two hose connections.
(4) An equally sized bypass around the pressure-regulating
device(s), with a normally closed control valve, shall be
installed.
(5) Pressure-regulating device(s) shall be installed not more
than 7 ft 6 in. (2.31 m) above the floor.
(6) The pressure-regulating device shall be provided with inlet
and outlet pressure gauges.
(7) The fire department connection(s) shall be connected to
the system side of the outlet isolation valve.
(8) The pressure-regulating device shall be provided with a
pressure relief valve in accordance with the manufacturer’s
recommendations.
(9) Remote monitoring and supervision for detecting high
pressure failure of the pressure-regulating device shall be
provided in accordance with NFPA 72, National Fire Alarm
and Signaling Code.
I may be reading it wrong, but I don't see this section as being applicable 
only when two hose connections are used.
Tony

On Wed, Sep 6, 2017 at 12:34 PM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
Read 7.2.4 closely:  “Where more than two hose connections are used downstream 
of a pressure-regulating device …”

A floor control assembly or a single hose connection with integral PR device 
does not require redundancy or a bypass because that section of the standard 
only applies to multiple hose connections influenced by a single PR device.

My opinion only, but the standard clearly says what is says …

SL

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Tony Silva
Sent: Wednesday, September 06, 2017 11:27 AM
To: 
[email protected]<mailto:[email protected]>
Subject: PRV By-pass

NFPA 14, 2010, 7.2.4 (4) requires a bypass across a prv. Is it only when 
multiple smaller prv's are used instead of a larger prv, or whenever any prv is 
used?
My application is there is a prv at the floor control stations supplying 
combined sprinkler/standpipe. Would this prv need a by-pass?
The other question is will every prv need control valves upstream and 
downstream?
I know it is good engineering practice to have the valves and by-pass, but very 
often there is not much space inside the stairs. What is the general industry 
practice?
Thanks,
Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to