Not to mention as builts.


Steve


-------- Original message --------
From: Michael Hill <[email protected]>
Date: 10/6/17 7:58 AM (GMT-08:00)
To: [email protected]
Subject: RE: Calcs and tenant improvements

As I am sure you are aware, many jurisdictions adopt/modify the standards and 
seem to apply them differently. Most jurisdictions we work in require 
substantial safety factors when calculating base building sprinkler 
installations. The reasons given for these are usually “to allow field changes” 
and to “account for future tenant revisions”. For instance, you would only be 
required to calculate the most demanding area of the highest typical floor in a 
multi-story office building. Any tenants on lower levels that matched the 
original pipe sizing and spacing would not require new hydraulic calculations. 
That has gone away for many jurisdictions, as they now require new calculations 
on all tenant improvements.

On the flip side of this. I have been asked to calculate projects that I would 
have argued did not need them, as I was matching existing conditions that had 
already been proven by hydraulic calculations, only to find these areas to be 
more demanding.

I do not mind having to do calculations on every project. We are however, 
finding it difficult to obtain water flow information in a timely manner from 
several local jurisdictions.

Mike Hill

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Friday, October 06, 2017 10:41 AM
To: [email protected]
Subject: RE: Calcs and tenant improvements

It’s Friday so..,

Where does it say in 13 that you do Not provided calcs?

If I read 23.1.3 they are required no?

R/
Matt



Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Michael Hill
Sent: Friday, October 6, 2017 8:28 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Calcs and tenant improvements

It is because of scenarios like these, the AHJ require calculations for 
everything. It makes the ill informed/trained do what they should have done 
originally.

Mike Hill

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Friday, October 06, 2017 10:22 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Calcs and tenant improvements

This may not speak to your question in general terms, but has a third party 
planner viewer for a local fire department I have kicked two tenant 
improvements back and demanded couch recently.   one of them entailed the 
Edition of 11 sprinklers in an area that already had 10, that was being 
remodeled into small counseling cubicles. The end result was 21 sprinklers in a 
space  no larger than 1200 square feet. The submitter put a note on the plan 
saying that they were taking the exception of only counting sprinklers in 
separate fire areas, his badly flawed premise being that the non-rated walls 
forming the little rooms represented a fire area separation of sorts.

The other was a retail tenant Improvement in an existing Ordinary Hazard shell 
building where outlets were spaced at 120 square feet and originally designed 
for K5.6 sprinklers. The TI utilized extended coverage at 20 x 20. The 
submitter's reasoning was it was like for like because the hazard didn't change 
and there were fewer sprinklers.

Like everything else, we in the sprinkler community need to take ownership of 
what is still a low standard of care in our industry. On the AHJ side of the 
counter, we hope that common sense will prevail.


Steve


-------- Original message --------
From: Travis Mack <[email protected]<mailto:[email protected]>>
Date: 10/6/17 6:39 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Calcs and tenant improvements

Interesting to see what others run into. As far as the PE seal, that is 
jurisdiction specific. We have PE on staff and seal in jurisdictions that 
require.

This has just been something that has been popping up more and more. It was 
very rare in the past. We maybe calculated 1:100. Now I am seeing 3:5 requiring 
it for the jurisdictions I deal with.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Oct 6, 2017, at 6:31 AM, [email protected]<mailto:[email protected]> 
wrote:
It depends on the jurisdiction, but I do see it. More of the rule and not the 
exception. I don't see anything to the extreme you are talking about.

I did have one recently where the existing sprinklers were installed on flex 
drops and we have to move 5 sprinklers one pad over. The engineer stated if we 
used flex drops (even the existing ones), the system had to calculated. 
However, if we removed the flex and installed hard pipe, no calcs we're 
required.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)

On Oct 6, 2017 at 9:15 AM, <Travis Mack<mailto:[email protected]>> wrote:
How many of you are being required to calculate systems when you do a tenant 
improvement? Just your run of the mill add/relocate.

I am seeing it come up more and more. I am seeing it in situations where it is 
mostly relocates and no additions anywhere near the design areas. I have one 
now where the AHJ rejected for no calculations where the shell was OH2 and the 
new space is residential lofts. This particular AHJ wants us to show all piping 
on portions of the floor where no work is being done. They are also requiring 
us to submit plans for the two floors below our space that have no work being 
done.

Is anyone else seeing stuff like this?

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone
_______________________________________________ Sprinklerforum mailing list 
[email protected]<mailto:[email protected]>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to