The TYCO Royal Flush does speak of air flow around the plate in one section of 
the data sheet but it also shows a positive seal between the plate and ceiling 
when you purchase the gasketed cover. It’s detailed in the data sheet.

Viking’s cleanroom sprinkler cover assembly also has a built-in gasket to 
provide a positive seal.

You can’t have it both ways, a positive seal and free flow of air through the 
sprinkler between the cleanroom and ceiling space.

If you have airflow through the sprinkler you will not achieve certain level of 
cGMP, FDA or ISO standards.  But like stated before, the term Cleanroom covers 
a broad array of hygiene so in some cases a simple concealed sprinkler is more 
than adequate but in other cases a concealed sprinkler alone would not provide 
adequate infiltration protection.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Wednesday, October 18, 2017 5:00 PM
To: [email protected]
Subject: Re: Clean Room Sprinkler Options [EXTERNAL]

The listing of the concealed sprinkler requires airflow out the top of the 
clean room lid. I'm going through this now on a project and you cannot seal 
both sides. If you check with any concealed sprinkler manufacturer they will 
tell you that airflow out the top of the cup is required.

On Wed, Oct 18, 2017 at 4:31 PM Prahl, Craig/GVL 
<[email protected]<mailto:[email protected]>> wrote:
The cover is held on by solder tabs which melt and release the cover when the 
setpoint temperature of the cover plate is reached.

You can also purchase a dust and air seal to prevent air and dust from passing 
through the cover plate.




Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Mark Sornsin [FAR]
Sent: Wednesday, October 18, 2017 4:17 PM
To: 
'[email protected]<mailto:[email protected]>'
 
<[email protected]<mailto:[email protected]>>

Subject: RE: Clean Room Sprinkler Options [EXTERNAL]

I would also argue that unless the manufacturer declares that the ‘holes in the 
cup’ cannot be covered, then there may not really be an issue with regard to 
increased response time (even if the response actually equates more with SR).

Moreover, this is a clean room. If the sprinklers are activating it’s too late 
for the material/equipment in the clean room – they are providing life-safety 
benefits and controlling a fire to prevent spread to other parts of the 
building.  Does it REALLY matter if it is QR or SR?


[Visit our Website at www.SummitCoUS.com]<http://www.SummitCoUS.com>

Mark Sornsin
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL
Sent: Wednesday, October 18, 2017 7:26 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Clean Room Sprinkler Options

Cleanrooms come in various classifications.  In some cases, you cannot have a 
standard pendent sprinkler as it would create surfaces where dust and other 
foreign material could collect and would also be difficult to clean.

There is not a perfect sprinkler solution for cleanroom spaces but when you are 
dealing with pharmaceutical, food, or other consumable and/or regulated 
materials, the rules for hygiene restrict you from using the same sprinkler you 
might use at the grocery store.




Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Larry Keeping
Sent: Tuesday, October 17, 2017 11:55 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Clean Room Sprinkler Options [EXTERNAL]

I’m no expert on clean rooms or concealed sprinkler’s etc. and while  I think 
the dry sprinkler with the boot is an interesting concept, but I don’t think it 
is meant for that type of application. The brochure for the boot says it is 
intended predominantly for use with clearance holes through freezer ceiling 
structures.

I would advise against using any concealed (or recessed) type sprinklers in a 
clean room, because they are all vented. I understand this is because the heat 
from the fire is supposed to flow through the vents up into the ceiling space. 
Concealed sprinklers have that gap for the cover plate as part of the venting 
configuration.

Even the Reliable “sealing” concealed sprinkler, which seals off the cover 
plate gap is not allowed in ceilings which have positive pressure.

I’ve been told that the reason FM doesn’t sanction Q/R concealed sprinklers is 
because their testing has found that a Q/R concealed sprinkler’s sensitivity is 
roughly equal to a standard response sprinkler installed 12 inches below the 
ceiling. With this, if you interfere with sprinkler’s ability to vent up into 
the ceiling space, as with a boot tight to the cup (ie. with no clearance hole) 
or with insulation all around the sprinkler, you must be even more seriously 
degrading the sensitivity.

If it was up to me I’d use a standard pendant sprinkler in clean room 
applications.

Way-back-when, I did some work at Litton systems and they had a special custom 
fitting/escutcheon with a gasket to make a tight connection to the ceiling, so 
nothing could transfer from the concealed space into the clean room.

Larry Keeping

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL
Sent: October-17-17 4:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Clean Room Sprinkler Options

If you have a LH or OH criteria where the concealed heads can be used, one 
method that was approved by one of the big insurers for a similar installation 
used the TYCO DSB-2 dry sprinkler boot on the sprinkler drop.  The boot was 
placed over the drop and sealed against the upper side of the celling panel.  
The concealed sprinkler used the gasket option on the room side of the 
sprinkler.

This method according to the underwriter had been proven to stop any 
infiltration into the occupied space from the ceiling cavity.

But if you have an EH occupancy, then that’s another story.

I would highly recommend contacting the owner’s Risk Consultant or Insurance 
Underwriter or EOR for input or approval on any method proposed.

Since this could be a “H” occupancy I do certainly hope there is a qualified 
engineer involved in the project.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Larrimer, Peter A
Sent: Tuesday, October 17, 2017 3:16 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Clean Room Sprinkler Options [EXTERNAL]

Can anyone please assist with a recommendation for a “clean room” sprinkler 
where the clean rooms are designed to be negative pressure (for compounding 
dangerous drugs).

The concealed sprinkler cut sheets that I’ve looked at online generally say 
that the concealed heads cannot be used in negative pressure rooms (positive 
pressure plenums) and this is the type of room design that we require.  The 
FlexHead cleanroom ceiling sprinkler connection doesn’t appear to be easy to 
clean after installation.

What type of quick response sprinkler could be used in a negative pressure room 
that is readily and easily cleanable?  Users wanted to used concealed 
sprinklers as they thought that the concealed sprinklers would be easy to wipe 
down when necessary, but we don’t want to violate the installation instructions 
on the cut sheets that state that the concealed sprinklers can’t be used with 
positive pressure plenums (negative pressure rooms).

Thanks in advance.

Pete Larrimer
VA


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--

Benjamin Young
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to