Sounds like the submitter likely shouldn't be designing standpipes.

Before even thinking of answering, please provide height of building and 
whether Skokie FD has any particular equipment issues or published policies on 
standpipe design, particularly starting pressures at Class 1 connections.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thomas Reinhardt
Sent: Wednesday, November 01, 2017 12:09 PM
To: [email protected]
Subject: Standpipe Pressure Question.

Question for the forum. I have a complete renovation of a school. They are 
required to have 3 standpipes installed. The designers approached me and asked 
if one of the standpipes could have a reduced pressure. The reason is because 
then they would have to upgrade the electrical power to the pump. This in turn 
would make them upgrade the power for the backup generator. This would create 
an economic  problem for the school district. In researching NFPA 14. I found 
that the minimum residual pressure at 2.5 in. should be 100psi for each 
standpipe. Am I interpreting this correct. They asked that 1 standpipe be only 
65psi (doesn't sound correct). NFPA 14 says that standpipes shall provide 250 
gallons. All standpipie hose connections to be class 1 systems. Am I missing 
something. Thanks

Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
[email protected]<mailto:[email protected]>