Aside from the standpipe design, is there any way to get more psi without the 
electrical upgrade? I recently put in a soft start controller that lowered 
in-rush amperage enough to drop a backup generator size.

We also have a project where they opted for a small diesel pump and no back up 
generator.

Matt

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Stossel
Sent: Wednesday, November 01, 2017 2:17 PM
To: [email protected]
Subject: RE: Standpipe Pressure Question.

It has been my experience that the pressure requirement between 65psi and 
100psi varies from city to city and state to state.  Is the building a high 
rise? Can the standpipes be classified as manual wet and not automatic and be 
based on the pumper trucks capabilities from the FDC instead of the fire pumps?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thomas Reinhardt
Sent: Wednesday, November 1, 2017 3:09 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Standpipe Pressure Question.

Question for the forum. I have a complete renovation of a school. They are 
required to have 3 standpipes installed. The designers approached me and asked 
if one of the standpipes could have a reduced pressure. The reason is because 
then they would have to upgrade the electrical power to the pump. This in turn 
would make them upgrade the power for the backup generator. This would create 
an economic  problem for the school district. In researching NFPA 14. I found 
that the minimum residual pressure at 2.5 in. should be 100psi for each 
standpipe. Am I interpreting this correct. They asked that 1 standpipe be only 
65psi (doesn't sound correct). NFPA 14 says that standpipes shall provide 250 
gallons. All standpipie hose connections to be class 1 systems. Am I missing 
something. Thanks

Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
[email protected]<mailto:[email protected]>