When did 14 bring in the 100psi requirement?  93? (or is my imagination running 
in the wrong direction).  If the building was constructed prior to the 100psi 
requirement, is there an argument that you're maintaining the level of 
performance of the originally designed system?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thomas Reinhardt
Sent: 2017/11/01 3:09 PM
To: [email protected]
Subject: Standpipe Pressure Question.

Question for the forum. I have a complete renovation of a school. They are 
required to have 3 standpipes installed. The designers approached me and asked 
if one of the standpipes could have a reduced pressure. The reason is because 
then they would have to upgrade the electrical power to the pump. This in turn 
would make them upgrade the power for the backup generator. This would create 
an economic  problem for the school district. In researching NFPA 14. I found 
that the minimum residual pressure at 2.5 in. should be 100psi for each 
standpipe. Am I interpreting this correct. They asked that 1 standpipe be only 
65psi (doesn't sound correct). NFPA 14 says that standpipes shall provide 250 
gallons. All standpipie hose connections to be class 1 systems. Am I missing 
something. Thanks

Tom Reinhardt
Fire Inspector/Plan Reviewer