Any soffits over bathrooms or HVAC supply? We have done 20x20 sidewalls in 
places like this.

Matt

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ed.Tambini
Sent: Tuesday, November 21, 2017 6:20 AM
To: [email protected]
Subject: RE: [EXTERNAL] Interesting issue .. residential sprinklers ..

Use half of a riser clamp and put the pipe tight to the deck


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Tuesday, November 21, 2017 4:27 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Interesting issue .. residential sprinklers ..

I am working on a project with a lot of 20x20 rooms in dwelling units. I have a 
concrete deck so my piping will be exposed. I am trying to find a 20x20 
solutions but keep running in to road blocks. Maybe someone has an idea.

The way I see it, I need one of the following …


I need a residential pendent sprinkler that can be installed with a deflector 
distance from the deck greater than allowed by NFPA 13 OR I need a residential 
UPRIGHT sprinkler listed for 20x20 spacing OR I need a listed hanger attachment 
that will allow me to install 1" branch piping tight to a concrete deck.



And go.


John Irwin
DynaFire, Inc.