We had a similar situation and used the Reliable F1RES49 Pendent, which has a 
listing of 4”-8” down. Hopefully you have good water.


Taylor Schumacher, CET
Security Fire Sprinkler<http://www.j-berd.com/>
P.O. BOX 7308 | St. Cloud, MN 56302-7308
3308 Southway Drive | St. Cloud, MN 56301
Office: 320.656.0847 | [email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Tuesday, November 21, 2017 5:27 AM
To: [email protected]
Subject: Interesting issue .. residential sprinklers ..

I am working on a project with a lot of 20x20 rooms in dwelling units. I have a 
concrete deck so my piping will be exposed. I am trying to find a 20x20 
solutions but keep running in to road blocks. Maybe someone has an idea.

The way I see it, I need one of the following …


I need a residential pendent sprinkler that can be installed with a deflector 
distance from the deck greater than allowed by NFPA 13 OR I need a residential 
UPRIGHT sprinkler listed for 20x20 spacing OR I need a listed hanger attachment 
that will allow me to install 1" branch piping tight to a concrete deck.



And go.


John Irwin
DynaFire, Inc.