Well I have not run the calc, but I’ll have a 750GPM pump at about 135PSI
of head 100’ below this calc area. It looks like I will end up calculating
5 sprinklers … maybe 6



John Irwin

DynaFire Inc.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Travis Mack
*Sent:* Tuesday, November 21, 2017 9:54 AM
*To:* [email protected]
*Subject:* Re: [EXTERNAL] Interesting issue .. residential sprinklers ..



If you are truly 20x20, then you are looking at 67 psi with the 4.9 vs 13
psi with something like a Tyco EC-11. Do you have enough pressure where 50
psi is of no issue?

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Nov 21, 2017, at 7:46 AM, John Irwin <[email protected]> wrote:

Yes. That’s an option as well. I have a pump so I am not terribly worried
about the demand. However the difference in price between a residential
pendent and something like a Tyco EC-5 is over $10. And I’m looking at over
1,000 of these buggers.



John Irwin

DynaFire Inc.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *
Kyle.Montgomery
*Sent:* Tuesday, November 21, 2017 9:44 AM
*To:* [email protected]
*Subject:* RE: [EXTERNAL] Interesting issue .. residential sprinklers ..



Residential sprinklers are “permitted” in dwelling units, not “required”,
right? Couldn’t you use any one of a number of commercial QR extended
coverage sprinklers?



That might mess you up if you are trying to do a 4-sprinklers residential
calc… or it could help because you could get a larger K-factor and lower
starting pressure for 20x20.



-Kyle M



*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *John Irwin
*Sent:* Tuesday, November 21, 2017 4:27 AM
*To:* [email protected]
*Subject:* [EXTERNAL] Interesting issue .. residential sprinklers ..



I am working on a project with a lot of 20x20 rooms in dwelling units. I
have a concrete deck so my piping will be exposed. I am trying to find a
20x20 solutions but keep running in to road blocks. Maybe someone has an
idea.



The way I see it, I need one of the following …



I need a residential pendent sprinkler that can be installed with a
deflector distance from the deck greater than allowed by NFPA 13 OR I need
a residential UPRIGHT sprinkler listed for 20x20 spacing OR I need a listed
hanger attachment that will allow me to install 1" branch piping tight to a
concrete deck.



And go.





John Irwin

DynaFire, Inc.





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to