Yes, 11.3 of the latest edition.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Tuesday, November 21, 2017 7:11 AM
To: [email protected]
Subject: Re: [EXTERNAL] Interesting issue .. residential sprinklers ..

Check chapter 11. I don’t have the standard in front of me. But that has been 
in the standard for about 2-3 decades.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Nov 21, 2017, at 8:07 AM, John Irwin 
<[email protected]<mailto:[email protected]>> wrote:
I thought we were talking about the standard spray. But you’re correct. It does 
look like Reliable has the residential option to allow me to be greater than 4” 
from the deck.

I can’t find where NFPA 13 allows a 4 residential sprinkler calculation. I was 
starting to think that was only in 13R. Can you direct me to that code 
reference?

John Irwin
DynaFire Inc.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Travis Mack
Sent: Tuesday, November 21, 2017 10:02 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: [EXTERNAL] Interesting issue .. residential sprinklers ..

That gives you about 25 psi of friction loss. If you can make that work you are 
good with residential. Why 5-6 sprinklers if going with residential pendents? 
Are you not permitted to do the 4 residential sprinkler calc?
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Nov 21, 2017, at 7:58 AM, John Irwin 
<[email protected]<mailto:[email protected]>> wrote:
Well I have not run the calc, but I’ll have a 750GPM pump at about 135PSI of 
head 100’ below this calc area. It looks like I will end up calculating 5 
sprinklers … maybe 6

John Irwin
DynaFire Inc.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Travis Mack
Sent: Tuesday, November 21, 2017 9:54 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: [EXTERNAL] Interesting issue .. residential sprinklers ..

If you are truly 20x20, then you are looking at 67 psi with the 4.9 vs 13 psi 
with something like a Tyco EC-11. Do you have enough pressure where 50 psi is 
of no issue?
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Nov 21, 2017, at 7:46 AM, John Irwin 
<[email protected]<mailto:[email protected]>> wrote:
Yes. That’s an option as well. I have a pump so I am not terribly worried about 
the demand. However the difference in price between a residential pendent and 
something like a Tyco EC-5 is over $10. And I’m looking at over 1,000 of these 
buggers.

John Irwin
DynaFire Inc.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Kyle.Montgomery
Sent: Tuesday, November 21, 2017 9:44 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: [EXTERNAL] Interesting issue .. residential sprinklers ..

Residential sprinklers are “permitted” in dwelling units, not “required”, 
right? Couldn’t you use any one of a number of commercial QR extended coverage 
sprinklers?

That might mess you up if you are trying to do a 4-sprinklers residential calc… 
or it could help because you could get a larger K-factor and lower starting 
pressure for 20x20.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Tuesday, November 21, 2017 4:27 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Interesting issue .. residential sprinklers ..

I am working on a project with a lot of 20x20 rooms in dwelling units. I have a 
concrete deck so my piping will be exposed. I am trying to find a 20x20 
solutions but keep running in to road blocks. Maybe someone has an idea.

The way I see it, I need one of the following …


I need a residential pendent sprinkler that can be installed with a deflector 
distance from the deck greater than allowed by NFPA 13 OR I need a residential 
UPRIGHT sprinkler listed for 20x20 spacing OR I need a listed hanger attachment 
that will allow me to install 1" branch piping tight to a concrete deck.



And go.


John Irwin
DynaFire, Inc.


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to