Yeah I thought so as well but it’s one of those times when you think you
are sure you know something and then can’t find it and question yourself …



John Irwin

DynaFire Inc.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Travis Mack
*Sent:* Tuesday, November 21, 2017 10:11 AM
*To:* [email protected]
*Subject:* Re: [EXTERNAL] Interesting issue .. residential sprinklers ..



Check chapter 11. I don’t have the standard in front of me. But that has
been in the standard for about 2-3 decades.

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Nov 21, 2017, at 8:07 AM, John Irwin <[email protected]> wrote:

I thought we were talking about the standard spray. But you’re correct. It
does look like Reliable has the residential option to allow me to be
greater than 4” from the deck.



I can’t find where NFPA 13 allows a 4 residential sprinkler calculation. I
was starting to think that was only in 13R. Can you direct me to that code
reference?



John Irwin

DynaFire Inc.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Travis Mack
*Sent:* Tuesday, November 21, 2017 10:02 AM
*To:* [email protected]
*Subject:* Re: [EXTERNAL] Interesting issue .. residential sprinklers ..



That gives you about 25 psi of friction loss. If you can make that work you
are good with residential. Why 5-6 sprinklers if going with residential
pendents? Are you not permitted to do the 4 residential sprinkler calc?

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Nov 21, 2017, at 7:58 AM, John Irwin <[email protected]> wrote:

Well I have not run the calc, but I’ll have a 750GPM pump at about 135PSI
of head 100’ below this calc area. It looks like I will end up calculating
5 sprinklers … maybe 6



John Irwin

DynaFire Inc.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Travis Mack
*Sent:* Tuesday, November 21, 2017 9:54 AM
*To:* [email protected]
*Subject:* Re: [EXTERNAL] Interesting issue .. residential sprinklers ..



If you are truly 20x20, then you are looking at 67 psi with the 4.9 vs 13
psi with something like a Tyco EC-11. Do you have enough pressure where 50
psi is of no issue?

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Nov 21, 2017, at 7:46 AM, John Irwin <[email protected]> wrote:

Yes. That’s an option as well. I have a pump so I am not terribly worried
about the demand. However the difference in price between a residential
pendent and something like a Tyco EC-5 is over $10. And I’m looking at over
1,000 of these buggers.



John Irwin

DynaFire Inc.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *
Kyle.Montgomery
*Sent:* Tuesday, November 21, 2017 9:44 AM
*To:* [email protected]
*Subject:* RE: [EXTERNAL] Interesting issue .. residential sprinklers ..



Residential sprinklers are “permitted” in dwelling units, not “required”,
right? Couldn’t you use any one of a number of commercial QR extended
coverage sprinklers?



That might mess you up if you are trying to do a 4-sprinklers residential
calc… or it could help because you could get a larger K-factor and lower
starting pressure for 20x20.



-Kyle M



*From:* Sprinklerforum [
mailto:[email protected]
<[email protected]>] *On Behalf Of *John Irwin
*Sent:* Tuesday, November 21, 2017 4:27 AM
*To:* [email protected]
*Subject:* [EXTERNAL] Interesting issue .. residential sprinklers ..



I am working on a project with a lot of 20x20 rooms in dwelling units. I
have a concrete deck so my piping will be exposed. I am trying to find a
20x20 solutions but keep running in to road blocks. Maybe someone has an
idea.



The way I see it, I need one of the following …



I need a residential pendent sprinkler that can be installed with a
deflector distance from the deck greater than allowed by NFPA 13 OR I need
a residential UPRIGHT sprinkler listed for 20x20 spacing OR I need a listed
hanger attachment that will allow me to install 1" branch piping tight to a
concrete deck.



And go.





John Irwin

DynaFire, Inc.





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to