I have no doubt Roland will shoot this thing in the head by Lunch Time in Kansas, Tomorrow.
Richard Bradley Casterline.

Quoting "MFP Design, LLC" <[email protected]>:

No, you don’t ignore the obstruction. I agree with that. I was just pointing out that SxL is not always the same for spacing and calculations.







Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]



<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com

<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0> https://www.hightail.com/u/MFPDesign

LinkedIn: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0> https://www.linkedin.com/in/travismack



“The bitterness of poor quality remains long after the sweetness of low price is forgotten.”







From: Sprinklerforum [mailto:[email protected]] On Behalf Of Kyle.Montgomery
Sent: Sunday, December 3, 2017 2:03 PM
To: [email protected]
Subject: RE: [EXTERNAL] Re: Saw-Tooth Ceilings



That is true. (See 23.4.4.6.5) Thanks for pointing that out.



But that does not mean you can ignore the obstruction when determining the required discharge, right? That was the premise of the original question.



I’ll amend my previous statement to say the area used for determining minimum discharge should be APPROXIMATELY 210 square feet, based on the original question and the precise slope of the ceiling.



-Kyle M



From: Sprinklerforum [mailto:[email protected]] On Behalf Of MFP Design, LLC
Sent: Sunday, December 03, 2017 12:03 PM
To: [email protected] <mailto:[email protected]>
Subject: RE: [EXTERNAL] Re: Saw-Tooth Ceilings



Not necessarily. Remember the generic phrase: Space on the slope, calc on the flat. So, you may be at 130 sq ft on the slope, but if it translates to 110 sq ft on the flat, then you calc for 110 sq ft.



From: Sprinklerforum [mailto:[email protected]] On Behalf Of Kyle.Montgomery
Sent: Sunday, December 3, 2017 10:45 AM
To: [email protected] <mailto:[email protected]>
Subject: RE: [EXTERNAL] Re: Saw-Tooth Ceilings



I disagree, Brad. Whatever distances you use to determine S x L for spacing the sprinklers, the same distances must be used to determine area of coverage for hydraulic calculations. (NOTE: There are a few exceptions, such as when using the 'Small Room Rule').



I think that NFPA 13 spells it out pretty clearly:



23.4 Hydraulic Calculation Procedures



23.4.4 Calculation Procedure.



23.4.4.6 Design Densities



23.4.4.6.3: The area covered by any sprinkler used in hydraulic design and calculations shall be the horizontal distances measured between the sprinklers on the branch line and between the branch lines IN ACCORDANCE WITH 8.5.2.



8.5.2 Protection Areas per Sprinkler:



8.5.2.1: Determination of Protection Area of Coverage.



8.5.2.1.1 The protection area of coverage per sprinkler shall be determined as follows:



1.      …
2.      Between branch lines as follows:

a. Determine the perpendicular distance to the sprinkler on the adjacent branch line (or to a wall OR OBSTRUCTION in the case of the last branch line) on each side of the branch line on which the sprinkler is positioned. b. Choose the LARGER of either twice the distance to the wall OR OBSTRUCTION or the distance to the next sprinkler.
c.      Define dimension as L.



I think that based on these code sections, the answer to the original question is that the sprinklers should be calculated as A = S x L = 15’ x (2 x 7’) = 210 square feet. So minimum discharge would be 21 GPM for light hazard. And if it’s to be considered Ordinary Hazard, the heads should be spaced at about 9’-3” along the branch lines.



-Kyle M







-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] <mailto:[email protected]>
Sent: Thursday, November 30, 2017 3:15 PM
To: [email protected] <mailto:[email protected]>
Subject: [EXTERNAL] Re: Saw-Tooth Ceilings



Space the sprinklers like you were plumb-bobbing up.

Calculate the density like you were plumb-bobbing down.

B.

Quoting Michael Hill < <mailto:[email protected]> [email protected]>:



So you are saying that this is a series of 15 sloped ceilings one

after the other, not a single obstructed saw tooth ceiling.



I am not trying to be argumentative. I am trying to convince myself

that what I am being told to do is correct.



Mike Hill





-----Original Message-----

From: Sprinklerforum

[ <mailto:[email protected]> mailto:[email protected]] On Behalf Of

 <mailto:[email protected]> [email protected]

Sent: Thursday, November 30, 2017 4:02 PM

To: <mailto:[email protected]> [email protected]

Subject: Re: Saw-Tooth Ceilings



23.4.4.6 Deisign Densities

23.4.4.6.2, and for backup-

23.4.4.6.5.

You don't have walls Michael, you have a sloped ceiling.

The down-slope 'half' of the pattern is obstructed, be it sawtooth or not :).

Brad.



Quoting Michael Hill < <mailto:[email protected]> [email protected]>:



That section explains what to do once the maximum area of protection

is determined. I am still not convinced.

I agree that plenty of water is going to get to the fire, if needed.

More so as this is a UFC project, HC-2 occupancy, dry system,

0.20/3500.



Suppose there were walls that extended down to the floor at each end

of the ceiling that created a compartment (which is how I am viewing

this situation). In this case the compartment would be 240' x 8'.

8.5.2 tells me to take the distance from the wall, double it and

multiply by the distance between sprinklers in the other direction.

No mention of if the area is broken down into smaller compartments.



Does anyone know of a section in NFPA-13 that allows me to ignore the

obstruction when determining area of protection per sprinkler.



This is how I look at things when I do not agree with them. I figure

I am sitting on a witness stand somewhere (after the fire the

destroyed the building) and some insurance company's' lawyer is

saying "point to where it says you can do that".



Mike Hill



-----Original Message-----

From: Sprinklerforum

[ <mailto:[email protected]> mailto:[email protected]] On Behalf Of

 <mailto:[email protected]> [email protected]

Sent: Thursday, November 30, 2017 2:34 PM

To: <mailto:[email protected]> [email protected]

Subject: Re: Saw-Tooth Ceilings



I'm with Ron.

See NFPA 13-2016

23.4.4.6.2.

Brad.



Quoting Ron Greenman < <mailto:[email protected]> [email protected]>:



I'll agree the sprinkler knows nothing, but that is irrelevant. We

are working with a mathematical model that will, if all the rules

are followed, give us a reasonable degree of confidence that it will

perform to the design intended, which is, in this case, to keep a

fire contained within the most demanding design area (or any other

similar, but less demanding

area) for a specified duration. So for OH I can space my sprinklers

along the ceiling at a MAXIMUM of 15 ft apart, in any direction

perpendicular to the walls, which is a maximum square footage per

sprinkler of 225 square feet, and a MINIMUM of six feet between them

for a total square footage of 36. So given Mike's layout, he is well

within the parameters of this rule.

Now though we run into another rule which states we cannot EXCEED

130 square feet of floor area per sprinkler in OH so if we run our

sprinklers at 15' apart on the line we can have a MAXIMUM distance

between lines a fraction over 8.5 feet. Since the sawtooth creates a

"compartment," so to speak, because of the obstructive nature of the

"wall" the "compartment"

distances are 8x15 per sprinkler so he is well within the spacing

rules regarding "throw," and since his horizontal space coverage

area at the floor is less than 130 sqft per sprinkler he is within

the area limitation for OH. His density will be a minimum of 0.15

gallons/min/sqft and presuming he has enough pressure to push that

quantity of water through the system to the 13 (before adjustments

to the design area, if any) design sprinklers the system will

p[erform as desired. Back to the ignorant sprinkler. Will it adjust

to the 1.0'x7.5'x7.0'x7.5' layout and deliver exactly 0.15 gpm to

each square foot per minute? Of course not. What will happen though

is the system will supply enough water to up to 13 sprinklers

anywhere in the system to meet the design parameter (containment of

the fire to no more than 1500sqft). We can feel confident about this

since sprinkler systems have been doing so for over a hundred years

both in pipe schedule and hydraulically designed configurations. In

every system, there is a prize and that is containment or

suppression of a fire. There are several design methods to obtain

the prize and 13 is merely a prescriptive set of rules to get us

there. As long as we follow the rules we'll be alright. If we want

to play mathematician or fluid dynamicist then we'll cease to be

layout technicians and we'll get distracted and our eyes will stray from the prize.



On Thu, Nov 30, 2017 at 9:33 AM, Nick Maneen < <mailto:[email protected]> [email protected]> wrote:



You are correct.  The sprinkler does not know it needs to throw

water in mainly one direction.  It will be 15x14







*Nick Maneen, SET *



*c* 704.791.7789 <(704)%20791-7789>







*From:* Sprinklerforum [mailto:[email protected].

org] *On Behalf Of *Michael Hill

*Sent:* Thursday, November 30, 2017 12:30 PM

*To:* <mailto:[email protected]> [email protected]

*Subject:* RE: Saw-Tooth Ceilings







Yes, the actual floor area is about 120ft² per sprinkler. Each

sprinkler has to spray 7’-0” towards the next line. The next

sprinkler is within 1’-0” of the vertical portion of the ceiling

(which I am considering an

obstruction) and will not spray any further in that direction. The

water will hit the obstruction and fall straight down. I know the

sprinklers can cover that 7’-0” spray, but I need to make sure it

does so at the correct density. So for hydraulic purposes is the

spacing considered 120ft² or is it 210ft².







My take is that the sprinkler is 7’-0” form a wall or obstruction,

as the sprinkler has to spray 7’-0” to cover to the low portion of

the saw-toothed ceiling. L=14  and S=15. So hydraulically that

sprinkler has to cover 210ft². I would like to say it is covering

120ft² but I need to see where in NFPA-13 that it says I can do so.











Mike Hill







*From:* Sprinklerforum [mailto:[email protected].

org < <mailto:[email protected]> [email protected]>] *On Behalf Of

*Ron Greenman

*Sent:* Thursday, November 30, 2017 12:09 PM

*To:* <mailto:[email protected]> [email protected]

*Subject:* Re: Saw-Tooth Ceilings







If I'm understanding your description and question properly you are

covering about 116-117 sqft of floor area if one considers the 1'8"

rise at the tip of the tooth an obstruction, which I would, and

your "throw distance" along the slope is at 0-360 degrees=7.5'/90

degrees=7.0'/180

degrees=7.5 degrees/270 degrees=1.0'. That puts you within coverage

rules for OH, and throw range rules for SS sprinklers.







On Thu, Nov 30, 2017 at 8:33 AM, Michael Hill < <mailto:[email protected]> [email protected]> wrote:



I am working on a firing range that is going to have a saw-tooth

type ceiling installed. I have a question about determining maximum

protection area per sprinkler.







The vertical portion is 1’-8” tall with the distance from the high

point to the low point being 8’-0”, measured along the slope.

Sprinklers need to be spaced close to the vertical portion of the

ceiling, to protect them from stray projectiles. The sprinkler will

end up being about 7’-0” from the low point of the ceiling,

measured along the slope. The sprinklers are about 8’-0” apart, but

with a 1’-8” vertical portion of the ceiling between them.

Sprinklers are spaced 15’-0” apart along the branchline. See

attached sketch (if it came through).







Would the spacing be 15’ x 8’ or would it be 15’ x 14’?







I feel it should be 15’ x 14’ as any individual sprinkler needs to

cover 7’-0” in one direction, measured along the slope. I feel the

vertical portion of the ceiling is an obstruction and can almost

been interpreted as a wall that extends to the floor. I also

thought I needed to increase my design area for sloped ceiling for

this situation, but have since been shown the commentary in the

handbook that explains why it is not required for saw-toothed ceilings.

Maybe I am wrong about the spacing as well.



















Mike Hill









_______________________________________________

Sprinklerforum mailing list

<mailto:[email protected]> [email protected]

<http://secure-web.cisco.com/1Vc6OgMERp1kIlJb_GeTyjDCQ4WHsl43FCxjqiu55wyWfSe7mu895M8mQimA2LKtIAUGGM_pNPMPnkhrJubNqDteP7YKEixzPrM2uf49AheA0iDKvUX1wo573R5P_fxKJjqczX8In-Gbwu320WY7p8w9aV4kOcBZcSoJkPJj3blTJJurZ4zE3gVaj-ulFB5qWoOsrQKN9eSoj1MpfsVRm4LWGvTrZnY6y1E-h38Qtz9P4V1nqOKmVGBeef0GWR3m_gJ7aqD17Qa0ZNEUmz4_jIA/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler> http://secure-web.cisco.com/1Vc6OgMERp1kIlJb_GeTyjDCQ4WHsl43FCxjqiu55wyWfSe7mu895M8mQimA2LKtIAUGGM_pNPMPnkhrJubNqDteP7YKEixzPrM2uf49AheA0iDKvUX1wo573R5P_fxKJjqczX8In-Gbwu320WY7p8w9aV4kOcBZcSoJkPJj3blTJJurZ4zE3gVaj-ulFB5qWoOsrQKN9eSoj1MpfsVRm4LWGvTrZnY6y1E-h38Qtz9P4V1nqOKmVGBeef0GWR3m_gJ7aqD17Qa0ZNEUmz4_jIA/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.

org











--



Ron Greenman





 <mailto:[email protected]> [email protected]



253.576.9700 <(253)%20576-9700>







The Universe is monstrously indifferent to the presence of man.

-Werner Herzog, screenwriter, film director, author, actor and

opera director (1942-)



_______________________________________________

Sprinklerforum mailing list

<mailto:[email protected]> [email protected]

<http://secure-web.cisco.com/1Vc6OgMERp1kIlJb_GeTyjDCQ4WHsl43FCxjqiu55wyWfSe7mu895M8mQimA2LKtIAUGGM_pNPMPnkhrJubNqDteP7YKEixzPrM2uf49AheA0iDKvUX1wo573R5P_fxKJjqczX8In-Gbwu320WY7p8w9aV4kOcBZcSoJkPJj3blTJJurZ4zE3gVaj-ulFB5qWoOsrQKN9eSoj1MpfsVRm4LWGvTrZnY6y1E-h38Qtz9P4V1nqOKmVGBeef0GWR3m_gJ7aqD17Qa0ZNEUmz4_jIA/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler> http://secure-web.cisco.com/1Vc6OgMERp1kIlJb_GeTyjDCQ4WHsl43FCxjqiu55wyWfSe7mu895M8mQimA2LKtIAUGGM_pNPMPnkhrJubNqDteP7YKEixzPrM2uf49AheA0iDKvUX1wo573R5P_fxKJjqczX8In-Gbwu320WY7p8w9aV4kOcBZcSoJkPJj3blTJJurZ4zE3gVaj-ulFB5qWoOsrQKN9eSoj1MpfsVRm4LWGvTrZnY6y1E-h38Qtz9P4V1nqOKmVGBeef0GWR3m_gJ7aqD17Qa0ZNEUmz4_jIA/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.

org









--

Ron Greenman



 <mailto:[email protected]> [email protected]



253.576.9700



The Universe is monstrously indifferent to the presence of man.

-Werner Herzog, screenwriter, film director, author, actor and opera

director (1942-)







_______________________________________________

Sprinklerforum mailing list

<mailto:[email protected]> [email protected]

<http://secure-web.cisco.com/13gNqfBr0Hh-jnLdoQqpN_295RoArY8SthvsGnwP3> http://secure-web.cisco.com/13gNqfBr0Hh-jnLdoQqpN_295RoArY8SthvsGnwP3

NcCySctz5ZgFNMq9KzjG6OOqc4MPdeQxWtCmYaXo_SM-Uw2bKQ1ZjPIw4yBPPKJPVeY4c

_seR6qr-yvX7HOnwtNMfHSY4RFNRYIaqz8AWFlXHEfEaObjqEYBCqDS63wGnoKqYPWwm5

dINDACwbg8XJQfloiA73_tKGrvhziamsCLeIExdEP_gKwIF6nVnaKsPhq4aOVtqAnpNDP

SFkcoTThQUWj0E8XILgRaKP4giCYqyw/http%3A%2F%2Flists.firesprinkler.org%

2Flistinfo.cgi%2Fsprinklerforum-firesprinkl

er.org



_______________________________________________

Sprinklerforum mailing list

<mailto:[email protected]> [email protected]

<http://secure-web.cisco.com/13gNqfBr0Hh-jnLdoQqpN_295RoArY8SthvsGnwP3> http://secure-web.cisco.com/13gNqfBr0Hh-jnLdoQqpN_295RoArY8SthvsGnwP3

NcCySctz5ZgFNMq9KzjG6OOqc4MPdeQxWtCmYaXo_SM-Uw2bKQ1ZjPIw4yBPPKJPVeY4c

_seR6qr-yvX7HOnwtNMfHSY4RFNRYIaqz8AWFlXHEfEaObjqEYBCqDS63wGnoKqYPWwm5

dINDACwbg8XJQfloiA73_tKGrvhziamsCLeIExdEP_gKwIF6nVnaKsPhq4aOVtqAnpNDP

SFkcoTThQUWj0E8XILgRaKP4giCYqyw/http%3A%2F%2Flists.firesprinkler.org%

2Flistinfo.cgi%2Fsprinklerforum-firesprinkl

er.org







_______________________________________________

Sprinklerforum mailing list

<mailto:[email protected]> [email protected]

<http://secure-web.cisco.com/1wSXTWcUCqMe9WMmhQCcjewIB4zgsTBa2dQhcuKUgp> http://secure-web.cisco.com/1wSXTWcUCqMe9WMmhQCcjewIB4zgsTBa2dQhcuKUgp

xXsi2LiAKBDbukJxANtM76byuYueNXEjEKPpm35XNAetZOWtJyuZ-yoBsy1Oq1-mK54mqk

updGogQvszCDGkNc_1kC_kbu5qKyZKq3jYE4AJc_YTfA01oZE-jnkywacNi7as6ymjqwXD

md04MwjJq-gvBYZl1iGn8KjF_HEWccoFiAItw00KgTGrQyGv1D63YjZFRJwLyvIQ-3aMsh

TYw759ChF0mwAy-aJGljJmQ5Ghg/http%3A%2F%2Flists.firesprinkler.org%2Flis

tinfo.cgi%2Fsprinklerforum-firesprinkler.org



_______________________________________________

Sprinklerforum mailing list

<mailto:[email protected]> [email protected]

<http://secure-web.cisco.com/1wSXTWcUCqMe9WMmhQCcjewIB4zgsTBa2dQhcuKUgp> http://secure-web.cisco.com/1wSXTWcUCqMe9WMmhQCcjewIB4zgsTBa2dQhcuKUgp

xXsi2LiAKBDbukJxANtM76byuYueNXEjEKPpm35XNAetZOWtJyuZ-yoBsy1Oq1-mK54mqk

updGogQvszCDGkNc_1kC_kbu5qKyZKq3jYE4AJc_YTfA01oZE-jnkywacNi7as6ymjqwXD

md04MwjJq-gvBYZl1iGn8KjF_HEWccoFiAItw00KgTGrQyGv1D63YjZFRJwLyvIQ-3aMsh

TYw759ChF0mwAy-aJGljJmQ5Ghg/http%3A%2F%2Flists.firesprinkler.org%2Flis

tinfo.cgi%2Fsprinklerforum-firesprinkler.org







_______________________________________________

Sprinklerforum mailing list

<mailto:[email protected]> [email protected]

<http://secure-web.cisco.com/1wSXTWcUCqMe9WMmhQCcjewIB4zgsTBa2dQhcuKUgpxXsi2LiAKBDbukJxANtM76byuYueNXEjEKPpm35XNAetZOWtJyuZ-yoBsy1Oq1-mK54mqkupdGogQvszCDGkNc_1kC_kbu5qKyZKq3jYE4AJc_YTfA01oZE-jnkywacNi7as6ymjqwXDmd04MwjJq-gvBYZl1iGn8KjF_HEWccoFiAItw00KgTGrQyGv1D63YjZFRJwLyvIQ-3aMshTYw759ChF0mwAy-aJGljJmQ5Ghg/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org> http://secure-web.cisco.com/1wSXTWcUCqMe9WMmhQCcjewIB4zgsTBa2dQhcuKUgpxXsi2LiAKBDbukJxANtM76byuYueNXEjEKPpm35XNAetZOWtJyuZ-yoBsy1Oq1-mK54mqkupdGogQvszCDGkNc_1kC_kbu5qKyZKq3jYE4AJc_YTfA01oZE-jnkywacNi7as6ymjqwXDmd04MwjJq-gvBYZl1iGn8KjF_HEWccoFiAItw00KgTGrQyGv1D63YjZFRJwLyvIQ-3aMshTYw759ChF0mwAy-aJGljJmQ5Ghg/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to