Kyle - You are correct. It would be 15 X 14 (assuming they can not comply with
the beam rule)
You can space sprinkler to sprinkler with up to a 36 inch elevation change IF
and ONLY IF, you:
Are LH or OH (so does not apply to storage). And
You meet the beam rule.
8.6.4.1.3 (A) explicitly uses the phrase “considered a wall” when more than 36
inches.
(B) allows you to ignore if you can meet the beam rule so if you can’t, you
then treat it like a wall.
As you pointed out and quoted the text - Both sides of the sprinkler are
assigned the greater of either side. 7 on one side and 2 x 1 on the other
equates to 7 on BOTH sides.
This is the long standing methodology and ugly has it may be, that’s who we
have to dance with. I suspect everyone knows this but we can’t help wishing it
were prettier.
Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
Fire Sprinklers Saves Lives