Kyle - You are correct.  It would be 15 X 14 (assuming they can not comply with 
the beam rule)

You can space sprinkler to sprinkler with up to a 36 inch elevation change IF 
and ONLY IF, you:
        
        Are LH or OH (so does not apply to storage). And

        You meet the beam rule.

8.6.4.1.3 (A) explicitly uses the phrase “considered a wall” when more than 36 
inches.

(B) allows you to ignore if you can meet the beam rule so if you can’t, you 
then treat it like a wall.

As you pointed out and quoted the text - Both sides of the sprinkler are 
assigned the greater of either side.  7 on one side and 2 x 1 on the other 
equates to 7 on BOTH sides.

This is the long standing methodology and ugly has it may be, that’s who we 
have to dance with. I suspect everyone knows this but we can’t help wishing it 
were prettier. 


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Dec 5, 2017, at 6:51 AM, Kyle.Montgomery <[email protected]> wrote:
> 
> You guys are making a good case... I'm just having a hard time with it 
> because it's different than what I've been doing for 10 years. But as a 
> contractor, it would definitely be helpful if I was wrong in this instance 
> (i.e. save some money).
> 
> I wish some of the "Big Wigs" on this site would chime in with their opinions.
> 
> -Kyle M