I see nothing wrong with that. The beam is your "protection line" or
"wall". The heads are spaced properly in each area they are protecting. The
heads protecting 5'-0 to the beam (10'-0) are spaced along the branch line
properly for that coverage. And the heads throwing 7'-6 to the beam (15'-0)
are spaced along the branch line properly for that coverage. The floor area
is protected properly.


On Thu, Dec 21, 2017 at 4:00 PM, James Crawford <[email protected]>
wrote:

> We have been having a discussion in the office about the S&L rule for
> spacing of sprinkler heads. We received a sprinkler drawing with some
> spacing that we do not agree with, see below, but can find no specific
> direction in NFPA #13 (2013) that says it is wrong.
>
>
>
> Basic situation we have a small building with a 20’ bay and a 30’ bay.
> Ordinary hazard spacing.
>
>
>
> For the 20’ wide bay, we have2  lines spaced at 10’ apart , so we have 5’
> off the wall then 10’ between the next line and 5’ to the beam line, the
> heads are spaced at 13’ along these lines.
>
>
>
> Then we have a 30’ bay  where we have 2 lines spaced 15’ apart, 7’6 off
> the beam then 15’ between the heads then 7’6 to the wall, heads are spaced
> at 8’ along the line
>
>
>
> So our discussion is the sprinkler lines along the beam line which would
> be 5’-0” plus 7’-6” for 12’-6” between the line. The sprinkler heads in the
> 20’ bay are spaced at 13’-0”, so if we use the S&L rule these heads are
> spaced at 12’-6” x 13’-0” or 162.6 ft². Is this correct?
>
>
>
> And yes I know we could space the 30’ bay with 3 lines at 10’ apart and
> that is what I would do but it is not our design.
>
>
>
> Comments
>
>
>
> Thank you
>
>
>
>
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone  604-888-0318 <(604)%20888-0318>
>
> Fax 604-888-4732 <(604)%20888-4732>
>
> Cel 604-790-0938 <(604)%20790-0938>
>
> Email  [email protected]
>
> Web www.phaserfire.ca
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to