The beam is an obstruction that acts like a wall.  You’re covering floor
space, so as long as each sprinkler covers the correct area (30 sf), then
the spacing that you are describing sounds in compliance with NFPA 13
spacing rules.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of James Crawford
Sent: Thursday, December 21, 2017 3:00 PM
To: [email protected]
Subject: S & L Rule

 

We have been having a discussion in the office about the S&L rule for
spacing of sprinkler heads. We received a sprinkler drawing with some
spacing that we do not agree with, see below, but can find no specific
direction in NFPA #13 (2013) that says it is wrong.

 

Basic situation we have a small building with a 20’ bay and a 30’ bay.
Ordinary hazard spacing.

 

For the 20’ wide bay, we have2  lines spaced at 10’ apart , so we have 5’
off the wall then 10’ between the next line and 5’ to the beam line, the
heads are spaced at 13’ along these lines. 

 

Then we have a 30’ bay  where we have 2 lines spaced 15’ apart, 7’6 off the
beam then 15’ between the heads then 7’6 to the wall, heads are spaced at 8’
along the line

 

So our discussion is the sprinkler lines along the beam line which would be
5’-0” plus 7’-6” for 12’-6” between the line. The sprinkler heads in the 20’
bay are spaced at 13’-0”, so if we use the S&L rule these heads are spaced
at 12’-6” x 13’-0” or 162.6 ft². Is this correct?

 

And yes I know we could space the 30’ bay with 3 lines at 10’ apart and that
is what I would do but it is not our design.

 

Comments

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]

Web www.phaserfire.ca

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to