I beg your pardon *Allan.
B.
Quoting [email protected]:

That's awesome Allen.
I have often marveled at the fact that if Cad had occurred before Calcs, after we got spacing, location, and position right, we could have frozen the WALL and CEILING layers and sized every pipe in a matter of minutes!

Brad.

Quoting AKS-Gmail-IMAP <[email protected]>:

Be forewarned, this post describes ideas many would consider outrageous sprinkler design heresy. This “S&L Rule” discussion touches on a design rationalization problem that pops up in many scenarios. The problem often happens in OH spacing situations, but it can have variants in LH situations. The problem has some roots in the way NFPA 13 instructs how to determine sprinkler operational area using terms related to the physical layout of the sprinkler supply piping instead of concentrating solely on the sprinkler's relationship to other sprinklers and its surroundings. How piping reaches sprinklers has nothing to do with where a sprinkler operates, i.e. its operational area, yet NFPA 13 instructs to use S&L piping relationships to calculate that area. The proscribed method works most of the time but falls apart at other times. For example imagine a sprinkler layout where all the sprinklers are piped from a single point akin to a fantastical medusa head fitting. Or consider a layout where the sprinklers are piping from branch lines crisscrossed at random angles. Consider a radial sprinkler layout in a auditorium where all elements are arranged in concentric circles. Consider spaces where the lay-in ceiling grid is cocked at some angle to the walls, which might also be at some strange angle, where the structure above drives a branch line direction different to the ceiling. Consider a stagger sprinkler layout. And of course we have the irregular spaced beams condition this post thread is about. Irregular spaced beams can be the result of a change in beam span length being caused by the space itself changing width. The structure tightens the beam spacing instead of going with a deeper beam to handle the longer span. Now the sprinkler layout might have to account for both the room width change and the beam spacing change. The examples mentioned might seem impossible but I bet those that frequently have to deal with rationalizing a layout recognize how diverse conditions can get. Here are other examples of where S&L has difficulty. What is the operational area of a single sprinkler in free space were there are no walls? What is the operational area for the sprinklers arranged in a single line? These situations do arise. Consider a walkway above a ceiling. Consider huge orifice sprinklers where one in operation is listed to do the job. The standard now does have ways to rationalize those situations. The point is surely there is an operational area under these conditions. In other words there are locations underneath these sprinklers where the application density is at least some value when the sprinklers are operating at a set pressure. If a sprinkler operates in free space with no walls around it or if there are no sprinkler branch lines near it to witness the operation then does the sprinkler have an operational area? The preceding is intended to set the stage for the sprinkler design heresy part. Here it comes. The following two statements describe a way that rationalizes any sprinkler layout. The rationalization requires thinking about a sprinkler layout in an abstract way where the layout has multiple solution sets. “For any total group of sprinklers within a space there exists sets comprising of all the individual sprinklers operational areas where every individual operational areas do not exceed the maximum desired sprinkler design operational area. The set having the smallest maximum individual sprinkler operational area requires the lowest pressure to operate at the design application density.” In not so fancy terms the two statements boil down to allowing an imaginary boundary line between sprinklers to be manipulated such that no one sprinkler is required to have an operation area larger than the maximum for the intended design while maintaining the normal maximum and minimum spacing rules. Think of it as taking from Peter to give to Paul so that neither Peter or Paul, and all others in the set do not exceed the maximums at the minimum required pressure. This is sprinkler design heresy. NFPA 13 does not allow this thinking, yet NFPA 13 does dance around the idea in some instances, like the imaginary wall idea. The design heresy makes the beam problem a trivial rationalization. It provides a way to handle radial and horizontally curved layouts. It provides an easy way to handle stagger layouts, particularly space alterations to existing stagger layouts. It solves the problem where the wall between two perfectly fine, abutting OH systems is removed where the spacing in each system was different. The resulting spacing could be over spaced when the wall is removed, yet the spacing was perfectly fine before the wall was removed while at the same time the standard had no requirement for the original dividing wall. This is similar to the posted beam condition where one side is 10x13 and the other is 15x8. The design heresy eliminates the occasional additional sprinklers one has to add in OH situations where there are numerous layout considerations, like in a commercial kitchen or when on OH situation has to occur down a hallway that has indenting doorway entrances. Similar layout conditions arise in OH layout mechanical rooms that turn a corner. Many of these conditions result in sprinklers placed at locations where one is standing there at the site looking at sprinklers, the thought, “Sure looks like too many here.”, comes instantly to mind.
Allan Seidel
St. Louis, MO

On Dec 21, 2017, at 10:19 PM, [email protected] wrote:

"In order to form a more perfect thirteen" we play like walls are not there even when they are, and rated no less-- density/area method-- and we play like walls are there when they are not-- as in this and the recent 'saw-tooth type' ceiling discussions.
TC members have always kept it Conservative though so it's all good.
.

Quoting "MFP Design, LLC" <[email protected]>:

Larry:

I think the original question is asking what is the area of coverage of this setup. You have two lines that are 10' apart with sprinklers 13' on center on the lines. Call these lines A and B. Then in the adjacent bay, you have lines 15' on center with sprinklers 8' on center. Call these lines C and D.

The question is the sprinklers on branchline B. They are 13' on center going down the line. The next adjacent line C is 12'-6" away. So, basically, are the sprinklers on branch line B spaced at 13' x 10' (5' from the beam), or 13' x 12'6" (12'6 is the distance between the lines). If this dividing point was a full height wall, then there would be no question. But, the floor area is unobstructed as the sprinklers may or may not throw under this beam. What if the beam is 24" deep. With SSU's and being 5' from the beam with a 12" deflector, I can easily throw under that beam and get all floor area protected. Of course with the distance of 7'6 from the beam, I can cover all of the floor as well.

I have always used and always been taught to space them in the bay, end of story. I recall one job that had an AHJ that was asking for everything you can think of. This particular issue was one of them. We ended up agreeing to change what would have been the spacing on Branch line "B" in this example to have the sprinklers 10' on center. That way, using his 12'6" between sprinklers, being 10' on center kept things less than 130 sq ft.

So, in this example, the spacing along the branch line would be
Line A = 13' on center for sprinklers
Line B = 10' on center for sprinklers
Line C & D = 8' on center for sprinklers

Again, this goes against how I was taught to space the sprinklers and how I have always done it. I just see the reasoning behind the question. Does the answer change if you have a girder instead of a beam? Why or why not?

Merry Christmas to all and to all a good night!



Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

“The bitterness of poor quality remains long after the sweetness of low price is forgotten.”



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On Behalf Of Larry Keeping
Sent: Thursday, December 21, 2017 8:04 PM
To: [email protected]
Subject: RE: S & L Rule

Who said they wouldn't obstruct heat flow?
Because they are more than 7.5 ft apart it can be considered to be "unobstructed" construction. But of course they are obstructions.

With unobstructed construction the deflector distance has to be 1" to 12" below the ceiling.

You can't space the lines as if the beams don't exist. That is why the spacing is across the width of the bays. Since the lines are spaced 1/2 L off either side of them, you have sprinklers on either side of them as per 8.6.5.1.2 (2). Therefore you don't have to worry about the "Beam Rule (Table 8.6.5.1.2, and Figure 8.6.5.1.2(a)).

All I'm saying is that you can space to the beams, bay per bay. You can be 5 ft off in the 20 ft bay and 7.5 ft off in the 30 ft bay and under those conditions it doesn't matter whether the sprinklers can spray under the beams or not.

Larry

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected]
Sent: December-21-17 8:16 PM
To: [email protected]
Subject: Re: S & L Rule

But Larry, if the beams are not an obstruction to heat flow OR spray pattern, it's like they don't exist, no?
Brad.

Quoting Larry Keeping <[email protected]>:

You don't need to do anything special with the deflector distance.
As per 8.5.2.1.1 (2), the line spacing is to a wall or obstruction:

(2) Between branch lines as follows:
(a) Determine perpendicular distance to the sprinkler on the adjacent
branch line (or to a wall or obstruction in the case of the last
branch line) on each side of the branch line on which the subject
sprinkler is positioned
(b) Choose the larger of either twice the distance to the wall or
obstruction or the distance to the next sprinkler
(c) Define dimension as L

The is no argument that the beams that delineate the bays are
obstructions. Even if the spray can throw under it, that doesn't
change that consideration.

Larry Keeping


-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: December-21-17 5:53 PM
To: [email protected]
Subject: Re: S & L Rule

I recently learned that the beam only acts like a wall if you can't
throw under it, so get those deflectors way up there!
(Crow and Thunderbird rocks)

Merry Christmas Forum,

Brad.

Quoting Bob <[email protected]>:

The beam is an obstruction that acts like a wall.  You’re covering
floor space, so as long as each sprinkler covers the correct area (30
sf), then the spacing that you are describing sounds in compliance
with NFPA 13 spacing rules.



Thank you,



Bob Knight, CET III

208-318-3057



From: Sprinklerforum
[mailto:[email protected]]
On Behalf Of James Crawford
Sent: Thursday, December 21, 2017 3:00 PM
To: [email protected]
Subject: S & L Rule



We have been having a discussion in the office about the S&L rule for
spacing of sprinkler heads. We received a sprinkler drawing with some
spacing that we do not agree with, see below, but can find no
specific direction in NFPA #13 (2013) that says it is wrong.



Basic situation we have a small building with a 20’ bay and a 30’ bay.
Ordinary hazard spacing.



For the 20’ wide bay, we have2 lines spaced at 10’ apart , so we have 5’
off the wall then 10’ between the next line and 5’ to the beam line,
the heads are spaced at 13’ along these lines.



Then we have a 30’ bay  where we have 2 lines spaced 15’ apart, 7’6
off the beam then 15’ between the heads then 7’6 to the wall, heads
are spaced at 8’
along the line



So our discussion is the sprinkler lines along the beam line which
would be 5’-0” plus 7’-6” for 12’-6” between the line. The sprinkler
heads in the 20’
bay are spaced at 13’-0”, so if we use the S&L rule these heads are
spaced at 12’-6” x 13’-0” or 162.6 ft². Is this correct?



And yes I know we could space the 30’ bay with 3 lines at 10’ apart
and that is what I would do but it is not our design.



Comments



Thank you





James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]

Web www.phaserfire.ca



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to