That’s what I thought, just wanted to confirm. CMSA heads are eating my lunch 
with the calc’s……

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Thursday, February 15, 2018 4:31 PM
To: [email protected]
Subject: Re: ESFR Heads in Concrete Tee's

No go on the esfr sprinkler in that case. CMSA or CMDA.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Feb 15, 2018, at 2:29 PM, Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
Looking for some confirmation that ESFR heads cannot be used with concrete tee 
construction when the tee is 26” deep. Cut sheet says in this case you’d have 
to put them in each bay but also says heads can’t be closer than 8’, tee’s are 
6’ on center.