That’s what I thought, just wanted to confirm. CMSA heads are eating my lunch with the calc’s……
Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/> From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: Thursday, February 15, 2018 4:31 PM To: [email protected] Subject: Re: ESFR Heads in Concrete Tee's No go on the esfr sprinkler in that case. CMSA or CMDA. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Feb 15, 2018, at 2:29 PM, Brian Harris <[email protected]<mailto:[email protected]>> wrote: Looking for some confirmation that ESFR heads cannot be used with concrete tee construction when the tee is 26” deep. Cut sheet says in this case you’d have to put them in each bay but also says heads can’t be closer than 8’, tee’s are 6’ on center. Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org