I was under the impression that the 8’ minimum had to do with skipping when the 
fire plume is moved by the first head going off?

Matt


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Friday, February 16, 2018 8:46 AM
To: [email protected]
Subject: RE: ESFR Heads in Concrete Tee's

Mark-
I got a phone call yesterday from a member of one of the committees who 
essentially said the same thing. I’ve re-spotted heads using ESFR in each 
pocket over the storage area and the calc’s are much better, still need to find 
some more cushion somewhere. Thanks again for the response.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Sornsin [FAR]
Sent: Friday, February 16, 2018 9:41 AM
To: '[email protected]'
Subject: RE: ESFR Heads in Concrete Tee's

This may not be an FM job – and FM doesn’t use the term ESFR anymore, but…

I am familiar with an FM job where storage (aka ESFR) sprinklers were used in 
every tee space of concrete tee construction – they were 30” deep tees. The 
rule against not spacing sprinklers closer than 8’ didn’t apply because the 
tees prevented cold soldering. The trick however is that FM has a minimum 
design area for their storage sprinkler calculations (Despite the base design 
being 12 sprinklers at a given pressure).  That area is 12 x the minimum 
sprinkler coverage area of 64 sq.ft., which is 768 sq.ft.

I.e. if your design area does not meet 768 sq.ft. FM requires you add 
sprinklers until you reach that threshold.

Again, the main point here is that the minimum spacing is meant for adjacent 
sprinklers, but not those obstructed from each other by construction features – 
at least in FM’s opinion.


[Visit our Website at www.SummitCoUS.com]<http://www.SummitCoUS.com>

Mark Sornsin
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Thursday, February 15, 2018 3:29 PM
To: 
[email protected]<mailto:[email protected]>
Subject: ESFR Heads in Concrete Tee's

Looking for some confirmation that ESFR heads cannot be used with concrete tee 
construction when the tee is 26” deep. Cut sheet says in this case you’d have 
to put them in each bay but also says heads can’t be closer than 8’, tee’s are 
6’ on center.

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to