The cut sheet says I'd have to put heads in every channel, no-bueno. I have it 
designed using CMSA heads but the calc's are killing me.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Thursday, February 15, 2018 4:31 PM
To: [email protected]
Subject: RE: ESFR Heads in Concrete Tee's

Any way to offset the lines? I can't recall if that is allowed with ESFR's.

The last time I had a concrete T roof, I went with CMSA.

Matt


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Thursday, February 15, 2018 3:29 PM
To: 
[email protected]<mailto:[email protected]>
Subject: ESFR Heads in Concrete Tee's

Looking for some confirmation that ESFR heads cannot be used with concrete tee 
construction when the tee is 26" deep. Cut sheet says in this case you'd have 
to put them in each bay but also says heads can't be closer than 8', tee's are 
6' on center.

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to