So it seems the intent is that the K5.6 sprinkler should be the same response 
as the listing for EC sprinkler AT THE SPACING IT’S BEING USED.  In my 
particular case, the 18’x18’ spacing is listed as SR, so the K5.6 sprinkler 
should also be SR.  But what if I’m using this EC sprinkler MOSTLY at 18’x18’, 
but a few are being used to cover a smaller area of 14’x14’.  So now I’m using 
an EC sprinkler that are listed as both SR (18’x18’) and QR (14’x14’) in the 
same compartment (specifically allowed by the new 8.3.3.5 section in the 2016 
edition).  So should the K5.6 sprinks be QR or SR?  And let’s make it more 
complicated – let’s say the nearest EC sprinkler to the K5.6 sprinkler to the 
north is spaced at 18’x18’ (SR) and the nearest EC sprinkler to the south is 
spaced at 14’x14’ (QR).  

 

Ed

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Thursday, February 15, 2018 5:51 PM
To: [email protected]
Subject: Re: QR/SR Sprinklers

 

I would apply then 2016 edition to the 2013 ed as CLARIFICATION.  We added to 
answer your question.  It is NOT The thermal element. It is the listing of the 
sprinkler in order to be QR.  Keep in mind that it was only a cycle or two ago 
where there was NO restriction on mixing thermal sensitivity for new 
installations.  Modifying an existing systems had a restriction but not totally 
new (yea go figure).  We added it but didn’t think about the EC sprinkler 
having a fast response link but a SR rating (common at 20 X 20 but also smaller 
areas for lower temp. ratings).

 

Next question:  Can I use said 20 x 20 spaced EC sprinkler in a light hazard 
occupancy?

 

Roland

 

 

Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.    

Dallas, TX

http://www.firesprinkler.org

 

Fire Sprinklers Saves Lives

 

 





On Feb 15, 2018, at 2:28 PM, Ed Kramer <[email protected] 
<mailto:[email protected]> > wrote:

 

Reference section 8.3.3.2 of the 2013 edition of NFPA 13:  “Where QR sprinklers 
are installed, all sprinklers within a compartment shall be quick-response 
unless otherwise permitted in 8.3.3.3.”  Section 8.3.3.3 isn’t applicable for 
this question.

 

I’m protecting an OH II sales area with EC sprinklers spaced (mostly) at 
18’x18’.  This particular sprinkler is listed as SR at that spacing, but is 
listed as QR for 14’x14’ and smaller spacing.  This sales area has a small 20 
sf nook (not a separate compartment) that requires an additional sprinkler.  My 
intent is to protect that nook with a K5.6 sprinkler.

 

Should the K5.6 sprinkler be SR or QR?  

 

The answer is probably SR since the EC sprinklers are installed at a spacing 
that has a SR listing.  But that would be mixing a standard-response element 
with a fast-response element – something I’ve been led to believe is not cool.

 

The 2016 flavor of NFPA 13 has a new section 8.3.3.5 that allows mixing a SR 
listing with a QR listing as long as it’s the same sprinkler (and therefor both 
have the same fast-response element).

 

Anybody want to give their 2 cents?

 

Ed Kramer

Bamford Fire Sprinkler Co., Inc.

5134 Merriam Dr./Shawnee Mission, KS  66203

Phone: 913-432-6688  Fax: 913-432-5294  Cell: 785-766-4894

 <mailto:[email protected]> [email protected]

 

_______________________________________________
Sprinklerforum mailing list
 <mailto:[email protected]> 
[email protected]
 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to