All of the suggestions I've seen in this thread (Fig. 103, Unistrut clamps, etc.) are good offerings, but don't forget, those things are not listed, so to use them legitimately they need an engineer's certification, as per Section 9.1.1.2 of NFPA 13-2013.
Unless you can get an Eng. Cert. for it, I would avoid the riser clamp idea. A deluge system will develop some healthy thrust forces up and down the length of the main, which could bend the vertical support rods. Larry Keeping -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Mike B Morey Sent: March-14-18 2:49 PM To: [email protected] Subject: Re: Supporting pipe in bottom of pre-cast trench You might also look at the Anvil 103 depending on space available. Mike Morey CFPS 3229 • NICET S.E.T. 123677 Project Manager • Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive • Fort Wayne, IN • 46825 direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991 email [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org