You can come off the overhead system with a 1 ½" hose connection in a fully 
sprinklered building.  Here is a reference from 2009 IBC regarding stage hose 
connections... note the exception.  I think it is the same in the more current 
codes, just had this one handy.



 [F] 905.3.4 Stages. Stages greater than 1,000 square feet in area shall be 
equipped with a Class III wet standpipe system with 1 1/2-inch and 2 1/2-inch 
hose connections on each side of the stage.



Exception: Where the building or area is equipped throughout with an automatic 
sprinkler system, a 1 1/2-inch hose connection shall be installed in accordance 
with NFPA 13 or in accordance with NFPA 14 for Class II or III standpipes.



[F] 905.3.4.1 Hose and cabinet. The 1 1/2-inch hose connections shall be 
equipped with sufficient lengths of 1 1/2-inch hose to provide fire protection 
for the stage area. Hose connections shall be equipped with an approved 
adjustable fog nozzle and be mounted in a cabinet or on a rack.



I have found that many fire departments do not want these installed so worth 
checking...actually, State of MN amended out this section in their building 
code.





Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of MFP Design, LLC
Sent: Thursday, March 15, 2018 2:24 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: stages



I need to confirm something before I go over the deep end.  Well, maybe I 
already have.





With regard to the hose valves at the side of a true stage, are these to be 
treated as a standpipe where you need 250 gpm @ 100 psi provided through the 
FDC and routed on a separate system?  Or can you come off the overhead system 
and just add 50 gpm per hose valve for your inside hose requirements?









Travis Mack, SET



MFP Design, LLC



3356 E Vallejo Ct



Gilbert, AZ 85298



480-505-9271



fax: 866-430-6107



<mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com





<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi

gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4

2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2

FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com



<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo

ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b

4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166

77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>

https://www.facebook.com/pages/MFP-Design-LLC/92218417692



Send large files to us via:

<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta

il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C

14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2

wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

https://www.hightail.com/u/MFPDesign



LinkedIn:

<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked

in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%

7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L

sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

https://www.linkedin.com/in/travismack





"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."





-------------- next part --------------

An HTML attachment was scrubbed...

URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/4ed72f10/attachment.html>

-------------- next part --------------

A non-text attachment was scrubbed...

Name: image001.jpg

Type: image/jpeg

Size: 6420 bytes

Desc: not available

URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/4ed72f10/attachment.jpg>

_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



______________________________________________________________________

This email has been scanned by the Symantec Email Security.cloud service.

For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/adfca750/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to