You can come off the overhead system with a 1 ½" hose connection in a fully sprinklered building. Here is a reference from 2009 IBC regarding stage hose connections... note the exception. I think it is the same in the more current codes, just had this one handy.
[F] 905.3.4 Stages. Stages greater than 1,000 square feet in area shall be equipped with a Class III wet standpipe system with 1 1/2-inch and 2 1/2-inch hose connections on each side of the stage. Exception: Where the building or area is equipped throughout with an automatic sprinkler system, a 1 1/2-inch hose connection shall be installed in accordance with NFPA 13 or in accordance with NFPA 14 for Class II or III standpipes. [F] 905.3.4.1 Hose and cabinet. The 1 1/2-inch hose connections shall be equipped with sufficient lengths of 1 1/2-inch hose to provide fire protection for the stage area. Hose connections shall be equipped with an approved adjustable fog nozzle and be mounted in a cabinet or on a rack. I have found that many fire departments do not want these installed so worth checking...actually, State of MN amended out this section in their building code. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> -----Original Message----- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Thursday, March 15, 2018 2:24 PM To: sprinklerforum@lists.firesprinkler.org Subject: stages I need to confirm something before I go over the deep end. Well, maybe I already have. With regard to the hose valves at the side of a true stage, are these to be treated as a standpipe where you need 250 gpm @ 100 psi provided through the FDC and routed on a separate system? Or can you come off the overhead system and just add 50 gpm per hose valve for your inside hose requirements? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4 2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2 FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b 4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166 77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C 14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2 wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0> https://www.hightail.com/u/MFPDesign LinkedIn: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77% 7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0> https://www.linkedin.com/in/travismack "The bitterness of poor quality remains long after the sweetness of low price is forgotten." -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/4ed72f10/attachment.html> -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 6420 bytes Desc: not available URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/4ed72f10/attachment.jpg> _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/adfca750/attachment.html> _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org