I haven’t run into a situation where we have been allowed to tap off a sprinkler system. All of then ones I have seen require a new feed from the riser and a full standpipe calc. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell)
> > On Mar 15, 2018 at 3:57 PM, <Steve Leyton > (mailto:st...@protectiondesign.com)> wrote: > > > > What Reed said - it can be either a small hose connection or a standpipe. I > think small hose connection is the simplest classification and you add 50 GPM > to the POC (or to each of two depending on size/configuration of the stage). > It might also be worth a chat with the responding FD to see if you can get > relief from the installation of hose and nozzle. What we've done in the past > for some FDs is furnish a 2½" FHV with a 2½" x 1½" reducer and no hose. If > the FD ever needed more water out of the valve they could pump the FDC like > crazy. > > Highly unlikely these connections will ever be used in a real-world scenario > regardless of how they're configured but the code says what it says ... > > The preceding is my personal opinion only, > Steve Leyton > > -----Original Message----- > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of Reed A. Roisum, SET > Sent: Thursday, March 15, 2018 12:46 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: stages > > You can come off the overhead system with a 1 ½" hose connection in a fully > sprinklered building. Here is a reference from 2009 IBC regarding stage hose > connections... note the exception. I think it is the same in the more current > codes, just had this one handy. > > > > [F] 905.3.4 Stages. Stages greater than 1,000 square feet in area shall be > equipped with a Class III wet standpipe system with 1 1/2-inch and 2 1/2-inch > hose connections on each side of the stage. > > > > Exception: Where the building or area is equipped throughout with an > automatic sprinkler system, a 1 1/2-inch hose connection shall be installed > in accordance with NFPA 13 or in accordance with NFPA 14 for Class II or III > standpipes. > > > > [F] 905.3.4.1 Hose and cabinet. The 1 1/2-inch hose connections shall be > equipped with sufficient lengths of 1 1/2-inch hose to provide fire > protection for the stage area. Hose connections shall be equipped with an > approved adjustable fog nozzle and be mounted in a cabinet or on a rack. > > > > I have found that many fire departments do not want these installed so worth > checking...actually, State of MN amended out this section in their building > code. > > > > > > Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection > Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | > KFIengineers.com<http://www.kfiengineers.com> > > -----Original Message----- > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of MFP Design, LLC > Sent: Thursday, March 15, 2018 2:24 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: stages > > > > I need to confirm something before I go over the deep end. Well, maybe I > already have. > > > > > > With regard to the hose valves at the side of a true stage, are these to be > treated as a standpipe where you need 250 gpm @ 100 psi provided through the > FDC and routed on a separate system? Or can you come off the overhead system > and just add 50 gpm per hose valve for your inside hose requirements? > > > > > > > > > > Travis Mack, SET > > > > MFP Design, LLC > > > > 3356 E Vallejo Ct > > > > Gilbert, AZ 85298 > > > > 480-505-9271 > > > > fax: 866-430-6107 > > > > <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com > > > > > > <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi > > gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4 > > 2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2 > > FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com > > > > <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo > > ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b > > 4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166 > > 77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0> > > https://www.facebook.com/pages/MFP-Design-LLC/92218417692 > > > > Send large files to us via: > > <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta > > il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C > > 14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2 > > wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0> > > https://www.hightail.com/u/MFPDesign > > > > LinkedIn: > > <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked > > in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77% > > 7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L > > sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0> > > https://www.linkedin.com/in/travismack > > > > > > "The bitterness of poor quality remains long after the sweetness of low price > is forgotten." > > > > > > -------------- next part -------------- > > An HTML attachment was scrubbed... > > URL: > <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/4ed72f10/attachment.html> > > > -------------- next part -------------- > > A non-text attachment was scrubbed... > > Name: image001.jpg > > Type: image/jpeg > > Size: 6420 bytes > > Desc: not available > > URL: > <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/4ed72f10/attachment.jpg> > > > _______________________________________________ > > Sprinklerforum mailing list > > Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > > ______________________________________________________________________ > > This email has been scanned by the Symantec Email Security.cloud service. > > For more information please visit http://www.symanteccloud.com > ______________________________________________________________________ > > ______________________________________________________________________ > This email has been scanned by the Symantec Email Security.cloud service. > For more information please visit http://www.symanteccloud.com > ______________________________________________________________________ > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/adfca750/attachment.html> > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/cfb7b1ed/attachment.html> _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org