Just the opposite but your reasoning when viewed a little differently will help lock it down. The fire goes up the slope and does not spread out in the normal circle. This results in the adjacent sprinklers (from the channel with the heat) seeing much less of the heat. SO if they are closer to the channel (represented by a spacing of 8 ft) then a normal pressure but if further apart (longer activation time) then a higher pressure .
Roland Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> Fire Sprinklers Saves Lives > On Apr 17, 2018, at 11:28 AM, Jeff Normand <jeff.norm...@gmail.com> wrote: > > I agree that wording confuses me also. Perpendicular to slope. Been too long > since I've dealt with this and I have to look it up each time. But I'm > thinking it makes sense that the spacing would be up the slope - fire goes up > the slope - so no more than 8 feet apart up the slope.