Cecil,
  

  
Globe Sprinkler has been doing a lot of research on this as part of their new 
attic sprinkler line. SFPE did a webinar on this recently. They had some great 
video and current research on this topic. Check them out.   
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (ofc)
  
860-553-3553 (fax)
  
860-608-4559 (cell)
  
  
  
  

  
  
>   
> On Apr 23, 2018 at 5:21 PM,  <Sprinkler Academy - C Bilbo 
> (mailto:prodesigngr...@msn.com)>  wrote:
>   
>   
>     
>   
>
> Yo Everybody!    Been a while, but here goes nuthin'....
>
>   
>
>
>
>
>   
>
> In the Mid-90's, Central Sprinkler Company   in Lansdale, Pa did some 
> research as part of developing the Attic Sprinklers.    We needed a base for 
> meeting a standard of performance to see if the attic sprinklers could do 
> what sprinklers should do; Control the Fire.    So an entire roof top 
> structure was built in a parking lot to see how standard spray sprinklers 
> performed.    Well.... let's just say that the experiment had to be stopped 
> before the whole thing burnt to the ground.
>
>   
>
>
>
>
>   
>
> We were delighted (I say we.... I was over in the SprinkCAD division at the 
> time) anyway, the research guys were happy to see that the attic sprinklers 
> did what they were supposed to do. They accomplished control.    They had to 
> be spaced at 6' because any more than 30' of throw   and the sprinklers would 
> exceed the 400 sq ft max from NFPA 13. It worked!!   
>
>   
>
>
>
>
>   
>
> So with that   line of thinking, if we ran standard spray sprinklers up the 
> slope no more than 15' apart AND we limited the opposite direction to 8' in 
> between channels for   each set of trusses (120   sq ft)..... that would 
> work. The heat being guided up the channels created by the trusses could 
> successfully activate the standard spray sprinklers.
>
>   
>
>
>
>
>   
>
> There's a whole bunch more to the story, but that gives a basic idea of where 
> we were coming from as a committee.
>
>   
>
>
>
>
>   
>
> Now...... this was all based on a true story from 25 years ago..... the only 
> guy I know that could sharpen/change the details would be the guy that set up 
> and participated in those test, Mark Fessenden.
>
>   
>
>
>
>
>   
> It should be recognized that the above is my opinion as a member of the NFPA, 
> and has not been processed as a formal interpretation in accordance with the 
> NFPA Regulations Governing Committee Projects and should therefore not be 
> considered, nor relied upon, as the official position of the the NFPA, nor 
> any of their technical committees.
>   
>  Sincerely,
>   
>   
>  Cecil Bilbo, president
>  Academy of Fire Sprinkler Technology   
> New Classes All the Time (http://sprinkleracademy.com/design_course/)
>  Champaign, IL
>  217.607.0325
>   www.sprinkleracademy.com (http://www.sprinkleracademy.com)
>   ce...@sprinkleracademy.com (mailto:ce...@sprinkleracademy.com)
>   OUR STUDENTS SAVE LIVES!!
>   
>   
>   
>   
>     
> From:  Sprinklerforum  <sprinklerforum-boun...@lists.firesprinkler.org>  on 
> behalf of bcasterl...@fsc-inc.com  <bcasterl...@fsc-inc.com>
>   Sent:  Monday, April 23, 2018 3:26 PM
>   To:  sprinklerforum@lists.firesprinkler.org
>   Subject:  Re: Perpendicular to Slope / Attic   
>   
>   
>   
>   
> Thanks for reply Todd.
>  If somebody asked me, "should the 8' rule be applied for parallel to   
>  the slope when the channels run end to end" I would have to say, "no,   
>  because the book don't tell me so".
>  I gotta be able to cite numbers to myself though so I'll know in about   
>  a week whether or not I think the book should say apply it.
>   
>  Brad
>   
>  Quoting Fpdcdesign  <fpdcdes...@gmail.com>:
>   
>   >  SFPE hosted a webinar yesterday on Globe’s new attic protection   
>   >  scheme. They had some great video that explained a lot of what is   
>   >  being talked about here.
>   >
>   >
>   >
>   >    Todd G Williams, PE
>   >  Fire Protection Design/Consulting
>   >
>   >  Stonington, CT
>   >
>   >  860-535-2080 (ofc)
>   >
>   >  860-553-3553 (fax)
>   >
>   >  860-608-4559 (cell)
>   >
>   >
>   >
>   >
>   >
>   >
>   >
>   >>
>   >>  On Apr 20, 2018 at 3:19 AM,     <Bcasterline   
>   >>  (mailto:bcasterl...@fsc-inc.com)>    wrote:
>   >>
>   >>
>   >>
>   >>    It was pointed out to me off forum the literature cleary shows back to
>   >>  back cannot be used when the channels are running end to end.
>   >>  (Thanks again Ed).
>   >>  So, should the same '8 foot rule' be applied for parallel to the slope
>   >>  when the channels run end to end?
>   >>
>   >>  Thanks,
>   >>  Brad
>   >>
>   >>  Quoting bcasterl...@fsc-inc.com:
>   >>
>   >>   >    I was glancing through the literature of one of the Specialty 
> Attic
>   >>   >    Sprinkler makers (back-back at the peak) and none of the plan 
> views
>   >>   >    shows which way the channels were running so the delay in 
> activation
>   >>   >    for the rare case of channels running end to end can be neglected,
>   >>   >    apparently. The Fire always goes up fast enough and if that's good
>   >>   >    enough for attic sprks it should be good enough for SSU.
>   >>   >
>   >>   >    Brad
>   >>   >
>   >>   >    Quoting bcasterl...@fsc-inc.com:
>   >>   >
>   >>   >>    That paints a perfect motion picture Roland.
>   >>   >>    So we space for 8ft end to end, not eave to peak.
>   >>   >>    On the off chance the channels run end to end it might be a good
>   >>   >>    idea to go 8 eave to peak too?
>   >>   >>    I've modeled attic type head discharge patterns but it never
>   >>   >>    occurred to me to try and gain a better understanding of the 8ft
>   >>   >>    thing by modelling activation, and now thanks to you I don't have
>   >>   >>    to...
>   >>   >>    Gee thanks Roland,
>   >>   >>    Brad
>   >>   >>
>   >>   >>    Quoting Roland Huggins     <rhugg...@firesprinkler.org>:
>   >>   >>
>   >>   >>>    Just the opposite but your reasoning when viewed a little
>   >>   >>>    differently will help lock it down. The fire goes up the slope
>   >>   >>>    and does not spread out in the normal circle. This results in 
> the
>   >>   >>>    adjacent sprinklers (from the channel with the heat) seeing much
>   >>   >>>    less of the heat. SO if they are closer to the channel
>   >>   >>>    (represented by a spacing of 8 ft) then a normal pressure but if
>   >>   >>>    further apart (longer activation time) then a higher pressure .
>   >>   >>>
>   >>   >>>    Roland
>   >>   >>>
>   >>   >>>    Roland Huggins, PE - Senior VP Engineering
>   >>   >>>    American Fire Sprinkler Assn.
>   >>   >>>    Dallas, TX
>   >>   >>>     http://www.firesprinkler.org     
> <http://www.firesprinkler.org/>
>   >>   >>>
>   >>   >>>    Fire Sprinklers Saves Lives
>   >>   >>>
>   >>   >>>
>   >>   >>>
>   >>   >>>
>   >>   >>>>    On Apr 17, 2018, at 11:28 AM, Jeff Normand     
>   >>   <jeff.norm...@gmail.com>    wrote:
>   >>   >>>>
>   >>   >>>>    I agree that wording confuses me also. Perpendicular to slope.
>   >>   >>>>    Been too long since I've dealt with this and I have to look it 
> up
>   >>   >>>>    each time. But I'm thinking it makes sense that the spacing 
> would
>   >>   >>>>    be up the slope - fire goes up the slope - so no more than 8 
> feet
>   >>   >>>>    apart up the slope.
>   >>   >>
>   >>   >>
>   >>   >>
>   >>   >>    _______________________________________________
>   >>   >>    Sprinklerforum mailing list
>   >>   >>    Sprinklerforum@lists.firesprinkler.org
>   >>   >>     
>   >>   
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   >>   >
>   >>   >
>   >>   >
>   >>   >    _______________________________________________
>   >>   >    Sprinklerforum mailing list
>   >>   >    Sprinklerforum@lists.firesprinkler.org
>   >>   >     
>   >>   
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   >>
>   >>
>   >>
>   >>  _______________________________________________
>   >>  Sprinklerforum mailing list
>   >>  Sprinklerforum@lists.firesprinkler.org
>   >>   
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   >>
>   
>   
>   
>  _______________________________________________
>  Sprinklerforum mailing list
>  Sprinklerforum@lists.firesprinkler.org
>   http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>          _______________________________________________ Sprinklerforum 
> mailing list Sprinklerforum@lists.firesprinkler.org 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org  
>           