Even if in the 7 foot unit heater zone, with the possibility of a sprinkler
being activated? Would it be a lesser evil if a non-ESFR 286 deg.F
sprinklers having the same k factor as the ESFR sprinklers are used only
near the unit heaters with the rest of the system being ESFR?

Tony

On Wed, May 2, 2018 at 8:59 AM, Mike Hairfield <[email protected]> wrote:

> Use the 212 deg. ones.
>
>
> ASCOA used to make a 286 deg. one but they are out of business.
>
>
> Mike
>
>
> ------------------------------
> *From:* Sprinklerforum <[email protected]>
> on behalf of Tony Silva <[email protected]>
> *Sent:* Wednesday, May 2, 2018 10:57 AM
> *To:* [email protected]
> *Subject:* ESFR sprinklers near unit heaters
>
> Are there any ESFR sprinklers rated for 286 deg.F? If not, how would you
> locate them near unit heaters when it is next to impossible to maintain a
> minimum 7 feet clearance? How have others solved this problem?
>
> Tony
>